The AC powerwall has cooling, it is a liquid? Anyone know if the 5kw
continuous and 7kw peak limits change with multiple units?
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
> I think that this may have come up before, but I do not remember there
> being a resolution:
> Do you guys have any tips on becoming a Tesla dealer? We have people ask
> about it all the time, but we have not been able to get Tesla to respond.
> We have installed Sonnen, which is also a great system, but the up front
> expense scares many people away. We are located in upstate NY which may
> have something to do with it.
>
> Cheers,
> Dave
>
>
> *--*
>
>
> *Dave Tedeyan*
> *Senior Engineer*
>
> *Taitem Engineering, PC*
> 10 Verizon Lane, Lansing, NY 14882
> Voice: (607) 930-3481 x6
> www.taitem.com
>
> On Tue, Feb 13, 2018 at 10:36 AM, August Goers <august at luminalt.com>
> wrote:
>
>> Marco,
>>
>> Thanks for sharing, it is good to hear details from an installer who is
>> living with a Powerwall. We starting selling the Powerwall 2 in 2017 and
>> have worked up a large pipeline. We have about 20 installed so far, but
>> are
>> still waiting on utility permission to operate which is taking a long
>> time.
>> We have spent a good deal of time commissioning and testing each system.
>> For the most part, our experience has been good although the
>> commissioning
>> software and internet connectivity features have been buggy. Hopefully
>> those are issues that will be ironed out by Tesla. Otherwise, we've had
>> the
>> systems correctly operate in on-grid and off-grid modes with both
>> Solaredge
>> and SunPower Equinox AC coupled systems.
>>
>> We installed conventional lead acid battery backup systems for over 10
>> years and I can confidently say that Tesla's Powerwall and Gateway setup
>> is truly market-disruptive. The design flexibility of the Gateway setup,
>> the small size, minimal labor to install, and performance blow other
>> systems out of the water. I hope that other manufacturers are able to
>> catch
>> up with this type of design.
>>
>> Best,
>>
>> August
>>
>> *August Goers*
>>
>> Luminalt Energy Corporation
>>
>> o: 415.641.4000 <(415)%20641-4000>
>>
>> www.luminalt.com
>>
>>
>>
>> On Sat, Feb 10, 2018 at 12:23 PM, Marco Mangelsdorf
>> <marco at pvthawaii.com>
>> wrote:
>>
>>>
>>>
>>> *Aloha Wrenches,*
>>>
>>>
>>> *I thought I'd share my own experiences with the Powerwall as my
>>> company
>>> is now launching a program to add PW to existing NEM systems since the
>>> vast
>>> majority of them do not have storage which means that if the grid goes
>>> down, so does their PV system. (With the exception of the SMA SB line
>>> and
>>> their Secure Power Supply.)*
>>>
>>>
>>> *And no, I'm not a shill or toadie for Tesla.*
>>>
>>>
>>> *marco *
>>>
>>> *I wanted to walk my own talk. Before we launched adding Powerwall to
>>> existing Net Energy Metered solar electric systems, I wanted to make
>>> sure
>>> that what was promised on paper would work in the real world. I added
>>> Powerwall to my NEM system last year and have been monitoring and
>>> testing
>>> it during normal grid-on and grid outage modes. And Iâm very pleased
>>> to
>>> report that Powerwall has performed flawlessly and as expected.*
>>>
>>>
>>>
>>> *When used in a NEM system, Powerwall is programmed to be in
>>> âBackupâ
>>> mode. When utility power is on, Powerwall stands ready in a full state
>>> of
>>> charge for any power outage. During normal grid-on conditions, my
>>> Powerall
>>> takes about .6 kilowatt-hours every other day to stay fully charged.
>>> Over
>>> the course of the month, this Powerwallâs electricity consumption
>>> comes to
>>> about 9 kWhs or about $3/month at the current HELCO R rate.*
>>>
>>>
>>>
>>> *I have turned the utility power off to my home on a number of
>>> occasions
>>> in order to experience how Powerwall would perform in a simulated grid
>>> outage. When the grid goes down, my house effectively becomes a
>>> self-generating micro-grid. That is, my photovoltaic system (solar
>>> modules
>>> and inverters) and Powerwall (battery storage and integrated inverter)
>>> form
>>> a power grid with energy being created and stored and then consumed by
>>> my
>>> electric loads.*
>>>
>>>
>>>
>>> *Several things I noted from my simulated grid outages:*
>>>
>>> *· I purposefully overloaded Powerwall by turning on my
>>> electric
>>> dryer and electric oven at the same time. As expected, since the
>>> maximum
>>> output of Powerwall is 5 kilowatts, it shutdown. Meaning that all the
>>> power in my house went off. Within seconds, Powerwall reset itself and
>>> the
>>> power came back on, with the dryer and oven having shut down after the
>>> power went off. If power does not come back on after your Powerwall
>>> trips
>>> off, you will need to turn off those high-power loads and reset
>>> Powerwall
>>> by turning its black on-off switch, located on the right side of the
>>> unit,
>>> from on to off and then on again. The important takeaway: during a
>>> utility
>>> outage, you will need to be careful as far as operating heavy electric
>>> loads, especially 240 volt appliances both from the perspective of
>>> overloading your Powerwall and rapidly drawing down the battery
>>> capacity,
>>> especially at night.*
>>>
>>> *· The magic of frequency shifting. Without getting into too
>>> much techno-talk, this is the story of frequency shifting. Normal
>>> utility
>>> frequency is 60 hertz (Hz). PV inverters require the utility frequency
>>> to
>>> be at or near 60 Hz in order to operate. During a grid outage,
>>> Powerwall
>>> effectively establishes grid quality power (120/240 volts at 60 Hz),
>>> allowing a micro grid to operate with solar providing power to your
>>> house
>>> loads (during daylight hours) and charge Powerwall as needed. During
>>> the
>>> day with the loads being met by your PV system and Powerwall being at
>>> or
>>> near full state of charge (97-100 percent), Powerwall will shift the
>>> frequency from 60 to 66 Hz in order to turn off the PV inverter(s).
>>> That
>>> is, the PV inverter(s) see the frequency out of spec and shut down as
>>> theyâre expected and required to do. Why? Because with Powerwall at
>>> or
>>> near full and the house loads being met, thereâs nowhere for any
>>> additional
>>> solar generation to go. Powerwall will wait for its the state of
>>> charge to
>>> drop below 96-97 percent before shifting the frequency back to 60 Hz
>>> which
>>> allows the PV system to restart and generate solar power again. This
>>> frequency shifting can take place repeatedly over the course of the day
>>> depending on load demands, solar potential and Powerwall state of
>>> charge
>>> and is perfectly normal and does not damage the PV inverters.*
>>>
>>> *· **66 Hz and home appliances: when Powerwall is at 66 Hz,
>>> some
>>> of your house loads may be affected. What I and other Powerwall owners
>>> have noticed, while not a comprehensive list, can include: electronic
>>> clocks running fast, motors sounding different (microwave, washing
>>> machine,
>>> pumps), uninterruptible power sources (UPS) not charging and going into
>>> back-up power mode, appliances having a computer behaving unusually.*
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: http://www.mail-archive.com/re
>>> -wrenches at lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
More information about the RE-Wrenches
mailing list