[RE-wrenches] experience with the Tesla Powerwall

penobscotsolar at midmaine.com penobscotsolar at midmaine.com
Tue Feb 13 11:33:43 EST 2018


I would like to add my experience with Tesla so far.
We applied to be an installer in Maine more than a year ago. Beside
getting an initial email stating that they received our application, we
have not heard a word since. I have one client with a SolarEdge 7600
StorEdge who put a deposit down in March of 2017, with a prediction in his
acceptance letter of an April 2017 installation. Last week he asked for
his deposit back. He has gotten the run around from the company for a
year. I have not heard a word from them in my quest to be a Tesla
Powerwall installer.
Granted, this is in Maine, and we are not a high density state, but it
still would be professional for them to rely to experienced people who
want to install their product.
Again, as a qualifier, this is only my experience, but it is frustrating.

Daryl DeJoy
NABCEP Certified PV
Penobscot Solar Design
www.penobscotsolar.com
Island Solar
www.islandsolarbahamas.com


> Marco,
>
> Thanks for sharing, it is good to hear details from an installer who is
> living with a Powerwall. We starting selling the Powerwall 2 in 2017 and
> have worked up a large pipeline. We have about 20 installed so far, but
> are
> still waiting on utility permission to operate which is taking a long
> time.
> We have spent a good deal of time commissioning and testing each system.
> For the most part, our experience has been good although the commissioning
> software and internet connectivity features have been buggy. Hopefully
> those are issues that will be ironed out by Tesla. Otherwise, we've had
> the
> systems correctly operate in on-grid and off-grid modes with both
> Solaredge
> and SunPower Equinox AC coupled systems.
>
> We installed conventional lead acid battery backup systems for over 10
> years and I can confidently say that Tesla's Powerwall and Gateway setup
> is truly market-disruptive. The design flexibility of the Gateway setup,
> the small size, minimal labor to install, and performance blow other
> systems out of the water. I hope that other manufacturers are able to
> catch
> up with this type of design.
>
> Best,
>
> August
>
> *August Goers*
>
> Luminalt Energy Corporation
>
> o: 415.641.4000
>
> www.luminalt.com
>
>
>
> On Sat, Feb 10, 2018 at 12:23 PM, Marco Mangelsdorf <marco at pvthawaii.com>
> wrote:
>
>>
>>
>> *Aloha Wrenches,*
>>
>>
>> *I thought I'd share my own experiences with the Powerwall as my company
>> is now launching a program to add PW to existing NEM systems since the
>> vast
>> majority of them do not have storage which means that if the grid goes
>> down, so does their PV system.  (With the exception of the SMA SB line
>> and
>> their Secure Power Supply.)*
>>
>>
>> *And no, I'm not a shill or toadie for Tesla.*
>>
>>
>> *marco *
>>
>> *I wanted to walk my own talk.  Before we launched adding Powerwall to
>> existing Net Energy Metered solar electric systems, I wanted to make
>> sure
>> that what was promised on paper would work in the real world.  I added
>> Powerwall to my NEM system last year and have been monitoring and
>> testing
>> it during normal grid-on and grid outage modes.  And I’m very pleased
>> to
>> report that Powerwall has performed flawlessly and as expected.*
>>
>>
>>
>> *When used in a NEM system, Powerwall is programmed to be in
>> “Backup”
>> mode.  When utility power is on, Powerwall stands ready in a full state
>> of
>> charge for any power outage.  During normal grid-on conditions, my
>> Powerall
>> takes about .6 kilowatt-hours every other day to stay fully charged.
>> Over
>> the course of the month, this Powerwall’s electricity consumption
>> comes to
>> about 9 kWhs or about $3/month at the current HELCO R rate.*
>>
>>
>>
>> *I have turned the utility power off to my home on a number of occasions
>> in order to experience how Powerwall would perform in a simulated grid
>> outage.  When the grid goes down, my house effectively becomes a
>> self-generating micro-grid.  That is, my photovoltaic system (solar
>> modules
>> and inverters) and Powerwall (battery storage and integrated inverter)
>> form
>> a power grid with energy being created and stored and then consumed by
>> my
>> electric loads.*
>>
>>
>>
>> *Several things I noted from my simulated grid outages:*
>>
>> *·         I purposefully overloaded Powerwall by turning on my
>> electric
>> dryer and electric oven at the same time.  As expected, since the
>> maximum
>> output of Powerwall is 5 kilowatts, it shutdown.  Meaning that all the
>> power in my house went off.  Within seconds, Powerwall reset itself and
>> the
>> power came back on, with the dryer and oven having shut down after the
>> power went off.  If power does not come back on after your Powerwall
>> trips
>> off, you will need to turn off those high-power loads and reset
>> Powerwall
>> by turning its black on-off switch, located on the right side of the
>> unit,
>> from on to off and then on again.  The important takeaway: during a
>> utility
>> outage, you will need to be careful as far as operating heavy electric
>> loads, especially 240 volt appliances both from the perspective of
>> overloading your Powerwall and rapidly drawing down the battery
>> capacity,
>> especially at night.*
>>
>> *·         The magic of frequency shifting.  Without getting into too
>> much
>> techno-talk, this is the story of frequency shifting.  Normal utility
>> frequency is 60 hertz (Hz).  PV inverters require the utility frequency
>> to
>> be at or near 60 Hz in order to operate.  During a grid outage,
>> Powerwall
>> effectively establishes grid quality power (120/240 volts at 60 Hz),
>> allowing a micro grid to operate with solar providing power to your
>> house
>> loads (during daylight hours) and charge Powerwall as needed.  During
>> the
>> day with the loads being met by your PV system and Powerwall being at or
>> near full state of charge (97-100 percent), Powerwall will shift the
>> frequency from 60 to 66 Hz in order to turn off the PV inverter(s).
>> That
>> is, the PV inverter(s) see the frequency out of spec and shut down as
>> they’re expected and required to do.  Why? Because with Powerwall at
>> or
>> near full and the house loads being met, there’s nowhere for any
>> additional
>> solar generation to go.  Powerwall will wait for its the state of charge
>> to
>> drop below 96-97 percent before shifting the frequency back to 60 Hz
>> which
>> allows the PV system to restart and generate solar power again.   This
>> frequency shifting can take place repeatedly over the course of the day
>> depending on load demands, solar potential and Powerwall state of charge
>> and is perfectly normal and does not damage the PV inverters.*
>>
>> *·         **66 Hz and home appliances: when Powerwall is at 66 Hz,
>> some
>> of your house loads may be affected.  What I and other Powerwall owners
>> have noticed, while not a comprehensive list, can include: electronic
>> clocks running fast, motors sounding different (microwave, washing
>> machine,
>> pumps), uninterruptible power sources (UPS) not charging and going into
>> back-up power mode, appliances having a computer behaving unusually.*
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>




More information about the RE-Wrenches mailing list