[RE-wrenches] Older iCel System Lithium Ion Batteries
Sindelar Solar
Allan at sindelarsolar.com
Sat Feb 10 03:37:53 EST 2018
Gary, you might try an old-fashioned approach: bypass the controller to
send the array straight to the batteries until threshold voltage is
reached. More specifically, bypass one of the controllers; assuming 48,
60 or 72 Vnom depending on array. Let the other controller remain in
normal operation. Send the unregulated array to bring initial battery
voltage up; then the other controller takes over and the one that was
bypassed now is reconnected. Better if the unregulated array is the
smaller of the two, I would suspect.
What I'm suggesting will work with flooded lead-acid, and likely VRLA
lead-acid as well, as long as the unregulated array is taken out of the
system before voltage exceeds bulk. It may not work at all with these
Li-I, as I have no experience with restoring them. Daryl may well be
right about being unrestorable below a threshold voltage; also the
batteries may need an operational BMS to take a charge. So this is
perhaps just food for thought.
Allan
--
*Allan Sindelar*
allan at sindelarsolar.com <mailto:allan at sindelarsolar.com>
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*
On 2/9/2018 6:16 PM, Gary Rochlin wrote:
>
> Does anyone have any information or specifications for an older circa
> 2010-2012 iCel System Lithium Ion Battery. We are doing a repair on
> an older 48V Lithium Ion system consisting of 3-6 ICel batteries wired
> in parallel and 1 Xantrex 6848 and 2 Xantrex Conext MPPT 60 150 Solar
> Charge controllers. Via a surge from SCE system shut down and sat
> before we were called in. Batteries are sitting at 6.67V and the
> charge controller will not turn on unless the batteries are at 40V
> since at the time they were made for lead acid batteries. I’m looking
> at finding the way to charge the iCel batteries or goose the charge
> controller into thinking 40V are coming from the batteries. I think
> I’m making sense here.
>
> *Blue Sky Energy *
>
> g.rochlin@ <mailto:mtnrider at verizon.net>blue-sky-energy.com
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180210/05c9f6d7/attachment.htm>
More information about the RE-Wrenches
mailing list