[RE-wrenches] Looking for Solar Ready pedestal

William Miller william at millersolar.com
Thu Jan 25 20:21:32 EST 2018


Friends:



Thank you all for on-line and off-line replies.



There appears to be some confusion as to the term “Solar Ready.”  In my
understanding, this term applies to meter/main/combo panels that have
special provisions to allow for increased back-feed amperage.  This is
usually done by providing means to easily incorporate “line-side”
interconnection.  As a reminder for those not familiar, line-side is a
connection between the meter and the main disconnecting means.  Usually it
means a lug kit to easily connect prior to the main disconnecting means, or
even an integral breaker space connected to the line side.  The integral
breaker obviates the need for a collocated OPCD.  This is a very handy tool
for your design kit and I suggest if you are not familiar with this option
you might want to become so.  Here is one link
<http://download.schneider-electric.com/files?p_Reference=998-19598128_US&p_EnDocType=Brochure&p_File_Id=1267795961&p_File_Name=998-19598128_US_WEB.pdf>
and another link
<http://www.eaton.com/Eaton/ProductsServices/Electrical/ProductsandServices/Residential/GroupMeteringandMeterBreakers/SolarPowerCenters/index.htm>
to information about these devices.



Unfortunately the solar-ready equipment I have found are all wall-mount and
I need a pedestal.  Several people kindly sent links to garden variety
pedestals that do not have this “solar-ready” capability.



I am aware that one can down-size a main breaker, but I don’t believe it
responsible to do so without numerical support for that move.  In the
jurisdiction regulating this project, the authorities wisely require a
numerical analysis of the loads in the residence through the process
outlined in the NEC.  I have done this but it adds about two hours to the
project as you need to inspect the residence, plug the numbers into a
spreadsheet and create a presentation to insert into the building permit
application.  This is certainly an option, however.



In certain cases one can find the room to tap onto the conductors between
the meter socket and the main disconnect.  We have done this either by
bolting lugs to existing threaded holes in a bus set or by application of
insulation piercing taps on cable conductors.  One then needs to locate a
properly sized fused disconnected immediately adjacent to the meter socket
fed by properly sized conductors.  I have applied the tap-rule and had
plan-checkers allow this calculation methodology, although some have argued
on this forum they are not related concepts.



Lastly, just to cover every contingency, one can configure a service with a
discrete socket, main breaker load center and a separate fused disconnect
for the solar back-feed.  This would look like much like an agricultural or
industrial service from a previous era.



I hope the above over-verbosity clears up any misconceptions.  I appreciate
all of the input.



Sincerely,



William Miller





[image: Gradient Cap_mini]
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600



*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *frenergy
*Sent:* Thursday, January 25, 2018 8:36 AM
*To:* re-wrenches at lists.re-wrenches.org
*Subject:* Re: [RE-wrenches] Looking for Solar Ready pedestal



Dave,

            I would agree with you regarding the 175 amp main breaker
leaving plenty of headroom for power to a residence.  The only exception
I'm aware of around these parts (No. Sierra) is the all electric house that
also has a ground source heat pump with heat strips for back-up. If the
GSHP can't keep up and the heat strips kick in, you're looking at about a
third of that 175 amps going to just heating.  We've also done the swap to
175 amp and its worked, so far, but...

Bill

Feather River Solar Electric

Bill Battagin, Owner

4291 Nelson St.

Taylorsville, CA 95983

530.284.7849

CA Lic 874049

www.frenergy.net

On 1/25/2018 6:43 AM, Dave Tedeyan wrote:

Hi William,

It is unlikely that you will find a 200A panel with 60A of backfeed
capacity. You can reduce the main breaker to 175A though and then any 200A
panel would work. I have never seen any residence come any where close to
drawing that much current that it would trip. We do it fairly often and
have never had an issue. Then you get 65A of backfeed capacity.



Cheers,

Dave




*--*



*Dave Tedeyan*

*Senior Engineer*



*Taitem Engineering, PC*

10 Verizon Lane, Lansing, NY 14882

Voice: (607) 930-3481 x6

www.taitem.com



On Wed, Jan 24, 2018 at 1:28 AM, William Miller <william at millersolar.com>
wrote:

Friends:



I am working on a residential 1 phase project with a Solar Edge 10,000.  I
need to source a 200 amp meter/main with a 60 amp solar input capability.
This needs to be a free-standing pedestal.  All I am finding is wall mount
(surface or flush) units.



Anyone know if a pedestal unit with these capabilities?



Thanks in advance.



William Miller



[image: Gradient Cap_mini]
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600 <%28805%29%20438-5600>




_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org





_______________________________________________

List sponsored by Redwood Alliance



List Address: RE-wrenches at lists.re-wrenches.org



Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html



List rules & etiquette:

www.re-wrenches.org/etiquette.htm



Check out or update participant bios:

www.members.re-wrenches.org





-- 



[image:
https://ipmcdn.avast.com/images/icons/icon-envelope-tick-round-orange-animated-no-repeat-v1.gif]
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>

Virus-free. www.avast.com
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180125/cbc444e3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1777 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180125/cbc444e3/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1776 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180125/cbc444e3/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 7810 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180125/cbc444e3/attachment.gif>


More information about the RE-Wrenches mailing list