[RE-wrenches] AFCI Faults, SMA Inverters, Solectria RSB's, & RF Signals

Steven Lawrence lawrencesteven at gmail.com
Thu Jan 25 08:52:01 EST 2018


Hi James,

Is the solectria combiner actually combining strings so you have one input
into the SMA inverter?  If so, did SMA approve arc fault detection at that
high current?  From what I understand, arc fault detection doesn't work on
strings greater than 20A.

In the solectria box, I'm assuming there is a contactor in there, correct?
Do you have coils of wire inside from the power supply to the contactor?  I
have seen instances where coiled wire was generated the noise itself.  Is
the wire from the power supply to the contactor shielded?


From: James Rudolph <jamesrudolph99 at gmail.com>
>
>
> Aloha Wrenches,
>
> I have a issue I would like to throw at the group.
>
> We have a SMA 24000TL-US with a Solectria Rapid Shut Down Combiner.
> The inverter keeps faulting the AFCI. We megged the strings,and checked all
> connections on all components. So we are confident that the issue is not
> related, or connected to all of that. We also swapped out the RSB.
>
> I really can't disclose where the building is located because its military,
> and most of their IT infrastructure happens to be in this building as well.
>
> I know from research, and tech support that this happens sometimes with RF
> signals,metal roofs,and communications antennas,etc.
>
> SMA is suggesting we could re-run the stings so that we mitigate the
> possibility that the strings are picking up this noise and triggering the
> AFCI, or get clearance to disable that feature on the inverter.
>
> Due to safety issues I'm sure the last option is not on the table.
>
> We can also place any given sting on the combiner and it will work fine
> with no faults up to four stings. Once we place more than four strings on
> the combiner the inverter will fault.
>
> Since we are still on the 2008 NEC in Hawaii this is our first run in with
> the Rapid Shut Downs too. Maybe somehow this is tied into the issue?
>
> Anyone have thoughts, or experience with this type of issue?
>
>
> Mahalo Nui,
>
>
> *James B. Rudolph*
>
> *Hawaii Unifed*
>
> *Director of  Energy*
>
> *ES Electrician # 10816*
>
> *NABCEP Certified PV Installer # 091209-155*
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-
> wrenches.org/attachments/20180124/455d31c5/attachment-0001.html>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180125/791e2ba0/attachment.htm>


More information about the RE-Wrenches mailing list