[RE-wrenches] 1,000V combiners
Chris Mason
cometenergysystems at gmail.com
Tue Jan 23 15:34:59 EST 2018
The reason I need these inverters is we had two CL60 480V inverters with
bases, and they fell off the bases in the hurricane and filled with water.
They were good inverters but the bases were garbage and could not support
the inverters in high wind. Very disappointing as the arrays had only a
relatively small amount of damage.
I am planning on using the Symo 24 fused inputs directly, recabling to hard
wire the strings to the inverters. That's how we do all our European spec
systems, it's so much better to have all the strings present at the
inverter.
Thanks for your advice.
On Tue, Jan 23, 2018 at 11:40 AM, Connell Christopher <
Connell.Christopher at fronius.com> wrote:
> Hi Chris,
>
> Please note that US models on the Symo 24.0-3 come with integrated fusing
> on the terminal block, so what you are asking for may not be needed.
> SolarBos does make some rather nice pass thru combiners as well, the
> F6sk-1FF-4xp is the part number which we typically recommended. This is a
> “pass thru” version. There is a combiner version as well.
>
>
>
> Please note that the Fronius SnapInverter series (Galvo, Primo, Symo) are
> Nema4x, which have passed all required testing, including being sprayed
> with a hose with 65 GPM (Gallons per min) from a 1 inch nozzle from of 10
> feet for 5 minutes. Fronius International has investigated water ingress
> problems pertaining to our product. Statistics have shown that less than 1%
> of installations in the USA have experienced water ingress problems. The
> majority of these less than 1% of installations which experienced this,
> were found to be installation errors (over 90%). The problem is usually
> when there are multiple inverter installed on a site the same way, leading
> to multiple inverters with water ingress, (IE, Improper Torque on the
> datcom cover).
>
> If you have any questions, please contact me at technical support at
> 219-734-5500 <(219)%20734-5500>
>
> Thanks
>
> ------------------------------------------------------------
> -----------------------------
>
> Chris Connell
>
>
>
> / Team Leader
>
> / Technical Support Dept.
>
> / Fronius USA LLC
>
> / 6797 Fronius Drive / Portage, IN 46368/ USA
>
>
>
> / Main: +1 (219) 734-5500 <(219)%20734-5500>
>
> / Fax: +1 (219) 734-5502 <(219)%20734-5502>
>
> / *Connell.Christopher at fronius.com <Connell.Christopher at fronius.com>*
> / www.fronius.com
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
--
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician
www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180123/9c2c40ec/attachment.htm>
More information about the RE-Wrenches
mailing list