Daniel,
While the Meanwell has been a good choice for me at times, I have also run
across some of their converters which have an active cooling fan which is
steady on (no thermal control). This leaves a steady phantom load as well
as a fairly loud background drone. And their tech support did not
accurately portray these specs to me when I asked.
Howie

On Tue, Jan 16, 2018 at 3:06 PM, Daniel Young <dyoung at dovetailsolar.com>
wrote:

> Answers to questions:
>
>
>
> The batteries are Discover EVL16A-A batteries. A single string of 8: 390AH
> @48V nominal. We had one fail last year, showing a significantly raised
> internal resistance when tested under a load then under charge. There is
> another one showing signs of weakness, but currently under a 30A draw it is
> only 0.12V lower than the highest battery in the mix, and 0.05V from the
> average battery voltage. Readings were: 6.0, 5.88, 6.0, 5.93, 5.92, 5.91,
> 5.93, 5.94 using a 1500W space heater as a constant load during the test.
>
>
>
> There are more loads than just networking and security that the client
> just recently disclosed. Gotta love the added loads to the design. There is
> a satellite DVR, 2x4 camera webcam systems, cell modem, simplisafe security
> system, chest freezer, 4 wifi range extenders to serve the less reliable
> security camera system, and 26W LED dusk-dawn light. I have already talked
> to them about thinking hard on what items can be removed for the winter at
> least (DVR is going away, and one of the camera systems too, likely the one
> requiring the wifi range extenders). All other seasons the system is fine.
>
>
>
> As for the DC converter(s) we would get a voltage specific converter for
> any unique voltages, depending on the # of unique items, we would likely
> abandon that approach if it got to bee too complicated. But thank you to
> all that provided guidance there. The meanwell units seemed to have the
> right specs to do the job if we go that route. We would also install them
> using a LVD of some sort, set somewhere above the standard low voltage
> cutoff of the rest of the system. We would also only go this route if all
> AC loads could be removed by doing this, allowing us to remove the 36w idle
> draw of the Outback.
>
>
>
> With Regards,
>
>
>
> Daniel Young,
>
> NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
>
>
>
> Lead Systems Designer for:
>
> [image: Dovetail 2013 cmyk 300dpi.jpg]
>
> *www.dovetailsolar.com* <http://www.dovetailsolar.com/>
>
> Ph: 740-274-0139 <(740)%20274-0139>
>
>
>
> We’ve completed nearly 400 renewable energy projects!  Check out a few in
> our photo gallery:
> *http://www.dovetailsolar.com/Our-Work.aspx?path=commercial+-+solar+electric*
> <http://www.dovetailsolar.com/Our-Work.aspx?path=commercial+-+solar+electric>
>
> This email message and attachments are intended only for the addressee.
> It may contain information which is legally privileged, confidential and
> exempt from disclosure.  If you are not the intended recipient of this
> message, you may not disclose, print, copy or disseminate this message
> and/or the information contained in the message.  If you have received this
> message in error, please reply and notify the sender (only) and delete this
> message along with any attachments.  Unauthorized interception of this
> email is a violation of criminal laws and laws covering electronic
> communications privacy matters.
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Starlight Solar Power Systems
> *Sent:* Tuesday, January 16, 2018 11:08 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] Off grid DC Loads: DC Converter
>
>
>
> I too would like to know the make and model of batteries that are loosing
> capacity. In the past 5 years we have experienced abnormally high failures
> from 2 brands.
>
>
>
> Larry
>
> On Jan 15, 2018, at 2:00 PM, Jay <jay.peltz at gmail.com> wrote:
>
>
>
> Can you tell us:
>
>
>
> Battery make,model and size?
>
>
>
> Jay
>
> Peltz power.
>
>
> On Jan 15, 2018, at 12:32 PM, Daniel Young <dyoung at dovetailsolar.com>
> wrote:
>
> Hello Wrenches,
>
>
>
> I have a client that is running into an issue with his off grid system.
> The system is 3yrs old and they are starting to notice their AGM battery
> bank is loosing capacity, in reality they are noticing the generator is
> triggering more often. They want to try to lower the frequency of the
> generator triggering if possible.
>
>
>
> The system is not occupied during much of the winter (unconditioned, which
> further hurts the battery bank capacity), but the client has a security
> system with a cell modem installed and always on. This fortunately allows
> Optics-RE access, but unfortunately based on the FNDC shunt readings, is
> pulling a consistent 150w from the battery bank. Currently the network and
> security equipment is powered from standard wall-warts running on AC.
>
>
>
> I’d like to help the client extend the time between generator cycles by
> taking the network loads and powering them directly from the battery bank
> (the loads are all 12Vdc). Does anyone have any recommendations for a
> decent quality DC_DC converter that would be applicable? Given inverter
> losses and the efficiency of the typical wall-wart, I’d expect the running
> loads to be closer to 80-100w rather than the 150w we see now. The intent
> is to then take the inverter into search mode, or even switch it off, to
> remove the tare losses there, and also to take all the wasted power from
> the standard wall-warts and go to a single, more efficient dc power supply.
>
>
>
> Any recommendations on a good DC_DC converter are appreciated.
>
>
>
> With Regards,
>
>
>
> Daniel Young,
>
> NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
>
> Dovetail Solar and Wind
>
>
>
> __________________________
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.
> re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180116/95fbe97b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4343 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180116/95fbe97b/attachment.jpg>


More information about the RE-Wrenches mailing list