I have use an Astron 48-12V converter with good success. The one I have used
is the 4812-20, but they also make a less powerful one.
They are not small in form factor, but seem to be reliable.
http://www.astroncorp.com/dcdc.shtml
-Glenn
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Daniel Young
Sent: Monday, January 15, 2018 3:32 PM
To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Off grid DC Loads: DC Converter
Hello Wrenches,
I have a client that is running into an issue with his off grid system. The
system is 3yrs old and they are starting to notice their AGM battery bank is
loosing capacity, in reality they are noticing the generator is triggering
more often. They want to try to lower the frequency of the generator
triggering if possible.
The system is not occupied during much of the winter (unconditioned, which
further hurts the battery bank capacity), but the client has a security
system with a cell modem installed and always on. This fortunately allows
Optics-RE access, but unfortunately based on the FNDC shunt readings, is
pulling a consistent 150w from the battery bank. Currently the network and
security equipment is powered from standard wall-warts running on AC.
I'd like to help the client extend the time between generator cycles by
taking the network loads and powering them directly from the battery bank
(the loads are all 12Vdc). Does anyone have any recommendations for a decent
quality DC_DC converter that would be applicable? Given inverter losses and
the efficiency of the typical wall-wart, I'd expect the running loads to be
closer to 80-100w rather than the 150w we see now. The intent is to then
take the inverter into search mode, or even switch it off, to remove the
tare losses there, and also to take all the wasted power from the standard
wall-warts and go to a single, more efficient dc power supply.
Any recommendations on a good DC_DC converter are appreciated.
With Regards,
Daniel Young,
NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
Dovetail Solar and Wind
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180115/fe618e4b/attachment.htm>
More information about the RE-Wrenches
mailing list