[RE-wrenches] Adding generators to PV systems

Tump tump at swnl.net
Fri Jan 12 05:44:45 EST 2018


2 suggestions; the first is installing the GT inverter output on the utility side of the T switch 
( Manu’s recommended spot)
. The second is have the generator tech set the frequency a bit lower then 59.5 Hz. (57-58 Hz.) which is usually the lower spot where the GT inverters will latch on and begin to output. Make sure that this setting is noted on the generator so the next tech will leave it at this setting.
> On Jan 11, 2018, at 8:54 PM, Wayne Irwin <PureEnergySolar at hotmail.com> wrote:
> 
> Hello All,
> 
> We have several customers adding generators to their homes on which we have previously installed PV systems.
> Historically most generators didn't produce a clean enough 60Hz sinewave to get the inverters to feed back.
> However, with the generator technology improving and the introduction of inverter generators, I'm concerned that if the inverters feed back to the generator it will smoke the stator.
> 
> I'm wondering if any of you have any experience/issues?  If so, what solutions or recommendations do you have?
> 
> Thanks,
> 
> 
> Wayne Irwin,
> President
> License #CVC56695 
> State Licensed Solar Contractor
> Pure Energy Solar International Inc. 
> Wayne at PureEnergySolar.com <mailto:PureEnergySolar at hotmail.com> 
>  <http://pureenergysolar.net/>http://PureEnergySolar.com <http://pureenergysolar.com/>
> http://SolarChargingStation.net <https://solarchargingstation.net/>
> 352 377-6527 Office
> 352 336-3299 Fax
> 
> 
> The Sun Is Always Shining!
> 
> The content of this message is Pure Energy Solar Confidential. If you are not the intended recipient and have received this message in error, any use or distribution is prohibited. Please notify me immediately by reply e-mail and delete this message from your computer system. Thank you.
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> Tump at swnl.net <blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net>               www.SWNL.net <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                              
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180112/dd5142f0/attachment.htm>


More information about the RE-Wrenches mailing list