[RE-wrenches] GENERAC EcoGen 6kw problem
palumbo131m at gmail.com
palumbo131m at gmail.com
Tue Jan 9 16:18:52 EST 2018
Thank you all for your help. Ray gets the gold star long distance diagnostics award as it was simply a thin layer of ice underneath the air cleaner. I cleared that out and it started right up and ran in good shape.
Dave
Sent from my iPhone
> On Jan 9, 2018, at 3:35 PM, Chris Mason <cometenergysystems at gmail.com> wrote:
>
> If the unit is still under warranty, have any Generac dealer run through
> the diagnostics. The testing flow suggests rotor or stator problems, and
> there is a proscribed testing flow that needs to be performed. If it is
> determined to be a warranty issue, it will be fixed for you at no cost.
> If it is not under warranty, I would still have a dealer look at it. There
> are a large number of possible issues and you are going to spend a lot of
> time trying to find the problem. A Generac tech will likely find the
> problem in a few minutes unless it is a serious problem, in which case you
> were never going to find it.
> I'm a Generac tech so I can speak from some experience that this is likely
> not a simple issue.
>
>> On Mon, Jan 8, 2018 at 8:13 PM, David Palumbo <palumbo131m at gmail.com> wrote:
>>
>> I am troubleshooting a 6kw EcoGen LP gas generator in my neighborhood that
>> starts quickly
>> • but immediately shuts down with an “Under Voltage” shutdown alarm
>> • I can clear shutdown alarm and restart with same result. I tried this a
>> few times with same result. One of the start attempts included a back fire
>> before shutting down.
>> • Generator was recently run successfully for a few hours during a cold
>> snap. Started after several attempts at -10 F.
>> • According to the EcoGen manual this Under Voltage alarm is triggered “If
>> the generator voltage falls below 85% of nominal for more than 15
>> seconds”. This definitely isn’t happening as the generator starts as usual
>> but shuts down within one or two seconds.
>> I will check for fouled spark plugs tomorrow. Anything else that might be
>> the problem?
>>
>> David Palumbo
>> Independent Power LLC
>> Hyde Park, VT
>> 802-371-8678 voice or text
>>
>> Sent from Mail for Windows 10
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
> --
> Chris Mason
> NABCEP Certified Solar PV Installer™
> Solar Design Engineer
> Generac Generators Industrial technician
>
> www.cometsolar.com <http://www.cometenergysystems.com>
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
More information about the RE-Wrenches
mailing list