Can the programming change on its own? I shut it off after it ran two days ago at my neighbors and no one touched it before I started it today. Neighbors are away and no footprints in new snow.
Dave
Sent from Mail for Windows 10
From: maverick at mavericksolar.com
Sent: Monday, January 8, 2018 7:30 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] GENERAC EcoGen 6kw problem
Check to see if it’s programming matches its wired and expected voltage output configuration.
Sent from my iPhone
> On Jan 8, 2018, at 6:13 PM, David Palumbo <palumbo131m at gmail.com> wrote:
>
> I am troubleshooting a 6kw EcoGen LP gas generator in my neighborhood that starts quickly
> • but immediately shuts down with an “Under Voltage” shutdown alarm
> • I can clear shutdown alarm and restart with same result. I tried this a few times with same result. One of the start attempts included a back fire before shutting down.
> • Generator was recently run successfully for a few hours during a cold snap. Started after several attempts at -10 F.
> • According to the EcoGen manual this Under Voltage alarm is triggered “If the generator voltage falls below 85% of nominal for more than 15 seconds”. This definitely isn’t happening as the generator starts as usual but shuts down within one or two seconds.
> I will check for fouled spark plugs tomorrow. Anything else that might be the problem?
>
> David Palumbo
> Independent Power LLC
> Hyde Park, VT
> 802-371-8678 voice or text
>
> Sent from Mail for Windows 10
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list