[RE-wrenches] Concrete Tile Roof Solar Installation - Oregon - Engineering requirements
William Miller
william at millersolar.com
Tue Dec 19 11:16:23 EST 2017
Kirpal:
It seems to me this is a matter of defining "Flush-mount." I would call
any installation where-in the panels are within the perimeter of the roof,
parallel with the surface and not more than 10 or so inches from the
surface of the roofing material a flush-mount. A proper tile roof
installation satisfies this and should be allowed without engineering.
Here in smoky California we have lots of tile roofs. We have tried or
reviewed all of the tile mount solutions. We rejected Quickmount as
poorly designed and fabricated. The posts are hollow and the threads fail
much too easily. Hooks are out of the question for lack of uplift
resistance. Snap-N-Rack posts and flashings are too weakly built and
don't look like they will seal well. Our preferred roofer rejected them.
We settled on the robust DPW "Power Post" stanchions with two levels of
flashing. On these we set Snap-n-Rack 100 series rail. The Power Posts
are solid aluminum and allow two lags. However DPW had such a huge lead
time for Power Posts that we tooled up to fabricate our own. You could
check with DPW or Solar Rack Works.
The biggest weatherproofing complexity is the sub-roof--the paper under
the tile. It is the actual rain barrier while the tile is the UV barrier
and aesthetic treatment. Over time, the sub-roof will become brittle. It
is fine as long as you don't touch it. We try to never rely on caulk for
the rain barrier and caulk won't stick to old sub-roof anyway. Instead we
lap good quality paper under the next layer above and over the flashing
below. This means we would be lifting the existing paper and it tears.
Therefore we have a licensed roofer remove tile from eave-to-ridge and
rake-to-rake and install new sub-roof. We use Oatey 11830 flashings over
Power Posts, overlapping each course of paper. This requires some short
courses, but felt is cheap. Over the tile we use a wide base galvanized
flashing interleaved with flat tile or wide based aluminum flashing with
curved tile. The roofer replaces the tile after we set stanchions.
The licensed roofer adds thousands of dollars to any tile job but without
this process a roof leak is likely. I figure a roof leak could cost tens
of thousands of dollars so the arithmetic is pretty easy.
By the way, these are trade secrets so don't tell anyone.
William Miller
Lic 773985
millersolar.com
805-438-5600
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Kirpal
Sent: Tuesday, December 19, 2017 7:26 AM
To: RE-wrenches
Subject: [RE-wrenches] Concrete Tile Roof Solar Installation - Oregon -
Engineering requirements
Hi Folks! We don't get many jobs installing solar on concrete tile
roofs....there aren't many around here. In Oregon we are allowed to do an
engineer-less installation on metal and comp roofs when the array is flush
mounted to the roof. Concrete tile roofs don't fit into this scenario.
My engineer quoted me $650 for a report authorizing the installation.
Seems like this is way too expensive for a modest 5kW system. What are
others doing for concrete tile roof installs. Engineering required? We
usually use SnapNRack as our racking system. (will probably use
QuickMount Tile Replacement Flashings for this project) Other Oregon
installers - any advice on this hurdle? Not worried about the technical
installation just the cost and formality of getting an engineers stamp for
permits.
Thanks in advance!
Sunny Regards,
Kirpal Khalsa
Oregon LRT#25
NABCEP Certified PV Installation Professional Oregon Solarworks LLC
www.oregonsolarworks.com
541-299-0402
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
l
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list