[RE-wrenches] Outback inverter generator question
Chris Worcester
chris at solarwindworks.com
Sat Dec 16 23:16:08 EST 2017
Dial down the max AC input, to something like 16 A at 120 volts or less depending on elevation. Then you can use this small gen set. The gen dropping out of synch means a tune up at least is in its future, or like you say, worse.
Chris Worcester
Solar Wind Works
NABCEP Certified PV Installer
Office 530-582-4503
Cell 530-448-9692
Fax 530-582-4603
www.solarwindworks.com
chris at solarwindworks.com
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Ray
Sent: Saturday, December 16, 2017 7:32 PM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] Outback inverter generator question
They need to add a transformer to operate the generator at full power. As Jerry noted, running at 120 vac, they are only pulling off one leg of the generator. This unequal loading can damage the generator. I'm guessing they damaged both Hondas. A transformer will allow the generator to operate at 240 vac, and step down to 120 vac for the inverter input. At that point, a Honda 5 K becomes a decent match for that inverter. In its current state, they will just keep frying generators. Some generators offer full 120 vac output, like the Ecogen. Either way these folks need to spend some money on the right generator or a transformer and repair the old generators.
Ray Walters
On 12/16/2017 7:04 PM, Jerry Shafer wrote:
> Ron
> A 5 k 120/240 genny pushing a 24 volt 3500 watt sounds way over kill
> and only pushing one leg only will result in issues, have not seen
> them with hondas but have with others. No mate means no programming so
> it might be over throttling the little inverter. You did not say
> anything about the batteries so we cant do the math but with the miss
> match it is not surprising that there are issues. Is the a PS-1 type
> panel or anything besides the inverter. maybe its me but I don't see
> parts required to make this a safe system. the Gen set issues also fit
> if there was no proper programming done. these can be fun to get all
> fixed up right and doing what they are designed to do.
> Jerry
> 255 *24 = 6120 / 2 = 3060 / (5000/2) => a 20 amp 120 vac is 2400 with
> this as an example with not much to go on, with the battery bit IF the
> batteries were dead they would be charged in just over an hr. and NO l
> did not take any losses into account but this was with D-8 DCFLA not
> sealed AGM's
>
> On Sat, Aug 12, 2017 at 2:32 PM, Ron Young <solareagle at solareagle.com>
> wrote:
>
>> Have a client where I recently installed an Outback VFX3524 inverter
>> in June. He’s using a Honda generator and has recently started having issues.
>> He has been complaining that the inverter seems to be running hot but
>> I believe this is because he doesn’t have good ventilation around it.
>> He is probably also running high on the loads. He doesn’t have a Mate
>> so can’t identify the error. He is in a remote location and I am
>> currently unable to travel due to fire restrictions in my area (major BC wildfires).
>>
>> Here is his recent email:
>> -Seems the inverter is recognizing the power in as an issue, and
>> throwing an error.
>> -My existing 5000 Honda generator has been online with the unit since
>> you installed it.
>> -The last few days, when there is very little load, or the unit goes
>> to float, the generator goes into a high rpm.
>> -My existing 5000 Honda crapped out on me this morning, and holds a
>> low rpm, not putting out much power. Will run a tool, but still
>> won’t hold a higher rpm.
>> -I borrowed an identical 5000 Honda generator, and it seemed to be
>> doing fine for about 1.5 hours.
>> -Now it’s doing the same thing as the other generator. The inverter
>> system throws an error, the generator is taken offline, and the
>> generator rpm go up.
>> -If I manually manipulate the throttle not he generator lower, then
>> the inverter re-engages.
>>
>> What the heck could this be? I don’t want to fry the borrowed
>> generator, but we can’t systematically bypass the inverter, and the
>> house requires the power.
>>
>> Ron Young
>> earthRight - Solareagle
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
> .html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list