[RE-wrenches] Breaker trip
Mac Lewis
maclewis1 at gmail.com
Wed Dec 6 09:59:06 EST 2017
Yes, it's an air compressor, but it's tripping the charge controller
breaker, not an AC breaker.
On Dec 6, 2017 7:43 AM, "Daryl DeJoy" <penobscotsolar at midmaine.com> wrote:
> Hi Mac,
> Just off the top of my head I’d say you’ve likely got an air compressor
> with a high locked rotor rating, at least with the info you’ve provided.
>
> Daryl
>
> Sent from Mail for Windows 10
>
> From: Mac Lewis
> Sent: Wednesday, December 6, 2017 7:18 AM
> To: RE-wrenches
> Subject: [RE-wrenches] Breaker trip
>
> Hello wrenches,
>
> I've got a mysterious breaker tripping that I need some ideas on how to
> fix.
>
> Original system:
> Array 6 x 235W Kyocera modules
> 1 x Outback FM60 charge controller
> 1 x Magnum MS 4024 PAE inverter
>
> Upgraded system we stacked a second inverter to accommodate an air
> compressor:
> Array 6 x 235W Kyocera modules
> 1 x Outback FM60 charge controller
> *2 x Magnum MS 4024 PAE inverter*
>
> There have been no changes to the solar array, just to the inverter side of
> the system. We have been getting intermittent breaker tripping (a couple
> of weeks between) on the battery breaker side of the charge controller.
> The basics have been checked and rechecked. Torque is good on all sides of
> the breaker all the way to the battery bussing.
>
> The only thing that I can think of is that during a surge on the AC side
> its sucking enough current out of the charge controller caps to trip this
> breaker occasionally.
>
> Has anyone experienced this? The only way I can see to fix it is to go
> with a larger breaker ampacity, but maybe there is something better. Does
> anyone no how quickly the max current setting in the Outback can respond,
> would dropping this help?
>
> Thanks
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-Wrenches
mailing list