[RE-wrenches] SW inverter trivia
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Thu Nov 9 15:23:48 EST 2017
I remember William the X SW and the Trace SW before that:) I am not sure
if I qualify to say those were good times as I have always been offgrid by
several miles. The more the better!
Schneider and Outback have taken steps with their recent
inverter/chargers to keep that feed to the grid from happening. Several
inverter/chargers will do this. The CSW has a mode that keeps the grid V
higher (current flows) so the CSW can't back feed and get the user in
trouble. They all call it different things like xero export, self
consumption, and enhanced AC support. Most use the mppt to trigger. A sub
panel is fed with the loads that the user wants backed up and powered
when the sun is out. When the grid is gone the sub panel is on battery
power. When there is not enough sun the grid powers the balance to the
sub panel.
If anyone needs any of these old devices please contact me off line as
there is this storage shed of SW's and MX-60s :)
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
> Friends:
>
>
>
> Some of you may remember when the original Xantrex SW inverters were
> approved for grid-tie and then that approval was rescinded. Later they
> were re-approved but only with the add-on GTI boxes. Those were good
> times, werenât they?
>
>
>
> I have learned a little something about that recently that I thought I
> would share here. During the early 2000s PG&E transferred NEM
> record-keeping from regional centers to a centralized location. During
> that process, PG&E lost the files for a number of our customers. We
> discovered this when smart meters are installed and the system no longer
> mechanically accounts for power export. We have to lobby long and hard to
> reestablish NEM authorization. I have done so for many clients. If
> anyone
> else is in this position, I might be able to advise. Contact me off-line.
>
>
>
> My point is that , in investigating the most recent case, we discovered
> that the SW inverter exports power even when the Sell function is
> disabled. The amount we recorded was about 200 watts for a 2 kw system
> mid-morning in October. This system did not have the GTI interfaces. I
> suspect the GTI units were developed in part to resolve this defect.
>
>
>
> This may not affect many of you, but if the subject comes up, now you
> know.
>
>
>
> Sincerely,
>
>
>
> William Miller
>
>
>
>
>
> [image: Gradient Cap_mini]
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
More information about the RE-Wrenches
mailing list