[RE-wrenches] Wattage 1/2 HP vs 1HP septic pumps

Chris Mason cometenergysystems at gmail.com
Sun Oct 29 07:24:52 EDT 2017


If you can get the Class rating of the motor, it will tell you a lot about
the start current requirements of the pump.

On Sun, Oct 29, 2017 at 4:29 AM, Darryl Thayer <darylsolar1 at gmail.com>
wrote:

> Hi, Dana, I know you have a different situation using a sewage ejector
> (grinder pump) but I have a customer that has a 1/2 HP well pump.  I do not
> know the drawdown, I think it is 60 feet.  It runs from an Outback VFX
> 3648, and a 4000 Watt autotransformer standard across the line starter.  It
> has never failed to start.  Nor does it "blink the lights", (running since
> 2004?) It runs at 350 to 400 watts into a 20-gallon diaphragm tank
> operating from 40 to 60 PSI.  Using Egauge on the 10 Minute scale, the peak
> seems to be about 3x the running load or 1200 to1500 Watts lasting less
> than 1 second.  In providing a family of two adults, the well pump is not a
> dominating load.  On the other hand, I had a customer with a 1.5 HP pump
> that I could not reliably start on a similar setup with a single FX 3548.
> The Radian is, of course, a much bigger animal.
>
> On Fri, Oct 27, 2017 at 3:45 PM, Dave Angelini Offgrid Solar <
> offgridsolar at sti.net> wrote:
>
> > I am with Windy! Having 1/2 HP and up anywhere offgrid is a problem if it
> > does not soft start. It will cause dimmed LED's to flicker and just the
> > surges that really are avoidable. Use soft start! There is not a reason
> > these days to prove that a Radian or XW will start a motor that bangs the
> > inverter to start. The only case I make for large old pump tech like
> these
> > is if it is for a fire suppression pump, in addition to a nice 3/4 HP
> > Grundfos home water pump.
> >
> > Dave Angelini Offgrid Solar
> > "we go where powerlines don't"
> > http://members.sti.net/offgridsolar/
> > e-mail  offgridsolar at sti.net
> > text 209 813 0060
> >
> >
> > > Really good to hear & thanks Chris.
> > > I just installed this system at our new home that we will be showing
> as a
> > > demonstration home. I come from the late '80s days of PV and a 1 HP
> pump
> > > was a major no-no back when.
> > > *Windy passed along a soft start suggestion & I was going to put a time
> > > clock turning on from 10AM-2PM every day to utilize a fuller bank. I
> will
> > > look at the SOC option on the Radian, but it is 200+' away from the
> > septic
> > > controller and conduit is in the ground.
> > > We have a HUP 2500 AHR/48-volt bank & 6,400 watt of PV tracked in a n-s
> > > canyon that limits the PV collection to 5 hours on a December day, that
> > so
> > > far even running a 3/4 HP air compressor all day/every day-7 days a
> week
> > > has never dropped at night more than 5%.
> > >
> > > ------------------------------------------------------------
> > ----------------
> > > Dana Orzel                       Great Solar Works, Inc.
> > > 208.721.7003                       dana at solarwork.com
> > > Idaho Contractor - # 028765          Idaho PV # 028374
> > > NABCEP # 051112-136                       www.solarwork.biz
> > > "Responsible Technologies for Responsible People since 1988"
> > > ï   Please consider the environment before printing this email.
> > >
> > >
> > > -----Original Message-----
> > > From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> On
> > > Behalf Of Chris Mason
> > > Sent: Friday, October 27, 2017 5:51 AM
> > > To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> > > Subject: Re: [RE-wrenches] Wattage 1/2 HP vs 1HP septic pumps
> > >
> > > What's the problem with the 1H pump you anticipate? We live on a 8KW
> > > Radian and it's very robust. We have load management relay system to
> > > handle the dryer, it's only allowed to work above 95% state of charge.
> > > Since your lift station has range, i.e., it doesn't have to work every
> > > minute of the day, you can control it so it works only during a SOC
> range
> > > or Time of Day range. You can also turn off other loads so there is
> > enough
> > > power. If you run the lift pump during the night, there is less chance
> of
> > > a convection oven running at that time. Or mid morning when everyone is
> > at
> > > work. Having time control or SOC control is very handy.
> > >
> > > On Wed, Oct 25, 2017 at 9:37 PM, Dana <dana at solarwork.com> wrote:
> > >
> > >> Ok all you whiz kids, bozos, & bolos:
> > >>
> > >>
> > >>
> > >> If I have a septic lift pump [off grid ouch] at 1HP/240 vac/8-amps to
> > >> meet all the usual state required overkill in septic design & a ½
> > >> HP/240 vac/4.9-amp pump would do the same job but it will take 10%
> > >> more time to dose 800 gallons.
> > >>
> > >> Powered by an 8 KW Outback Radian inverter.
> > >>
> > >> From a load point of view and a 240-volt 3 phase wild AC well pump
> > >> limiting the overall surge and general wattage is the smartest move,
> > >> but; Which pump will use less overall power? We are using 240 volt to
> > >> utilize both inverters and drop the load on either half of the Radian
> > >> inverter.
> > >>
> > >> Is there a smarter lift pump to use? ECM motor? Permanent magnet?
> > >>
> > >>
> > >>
> > >> ------------------------------------------------------------
> > >> ----------------
> > >>
> > >> Dana Orzel                       Great Solar Works, Inc.
> > >>
> > >> 208.721.7003                       dana at solarwork.com
> > >>
> > >> Idaho Contractor - # 028765          Idaho PV # 028374
> > >>
> > >> NABCEP # 051112-136                       www.solarwork.biz
> > >>
> > >> "Responsible Technologies for Responsible People since 1988"
> > >>
> > >> P Please consider the environment before printing this email.
> > >>
> > >>
> > >>
> > >>
> > >>
> > >> _______________________________________________
> > >> List sponsored by Redwood Alliance
> > >>
> > >> List Address: RE-wrenches at lists.re-wrenches.org
> > >>
> > >> Change listserver email address & settings:
> > >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> > >>
> > >> List-Archive: http://www.mail-archive.com/
> re-wrenches at lists.re-wrenches
> > .
> > >> org/maillist.html
> > >>
> > >> List rules & etiquette:
> > >> www.re-wrenches.org/etiquette.htm
> > >>
> > >> Check out or update participant bios:
> > >> www.members.re-wrenches.org
> > >>
> > >>
> > >
> > >
> > > --
> > > Chris Mason
> > > NABCEP Certified Solar PV Installerâ„¢
> > > Solar Design Engineer
> > > Generac Generators Industrial technician
> > >
> > > www.cometsolar.com <http://www.cometenergysystems.com>
> > > 264.235.5670
> > > 869.662.5670
> > > Skype: netconcepts
> > > _______________________________________________
> > > List sponsored by Redwood Alliance
> > >
> > > List Address: RE-wrenches at lists.re-wrenches.org
> > >
> > > Change listserver email address & settings:
> > > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> > >
> > > List-Archive:
> > > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> > org/maillist.html
> > >
> > > List rules & etiquette:
> > > www.re-wrenches.org/etiquette.htm
> > >
> > > Check out or update participant bios:
> > > www.members.re-wrenches.org
> > >
> > >
> > > _______________________________________________
> > > List sponsored by Redwood Alliance
> > >
> > > List Address: RE-wrenches at lists.re-wrenches.org
> > >
> > > Change listserver email address & settings:
> > > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> > >
> > > List-Archive:
> > > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> > org/maillist.html
> > >
> > > List rules & etiquette:
> > > www.re-wrenches.org/etiquette.htm
> > >
> > > Check out or update participant bios:
> > > www.members.re-wrenches.org
> > >
> > >
> >
> >
> > Dave Angelini Offgrid Solar
> > "we go where powerlines don't"
> > http://members.sti.net/offgridsolar/
> > e-mail  offgridsolar at sti.net
> > text 209 813 0060
> >
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> > org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> >
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts


More information about the RE-Wrenches mailing list