[RE-wrenches] Wattage 1/2 HP vs 1HP septic pumps
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Fri Oct 27 16:45:56 EDT 2017
I am with Windy! Having 1/2 HP and up anywhere offgrid is a problem if it
does not soft start. It will cause dimmed LED's to flicker and just the
surges that really are avoidable. Use soft start! There is not a reason
these days to prove that a Radian or XW will start a motor that bangs the
inverter to start. The only case I make for large old pump tech like these
is if it is for a fire suppression pump, in addition to a nice 3/4 HP
Grundfos home water pump.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
> Really good to hear & thanks Chris.
> I just installed this system at our new home that we will be showing as a
> demonstration home. I come from the late '80s days of PV and a 1 HP pump
> was a major no-no back when.
> *Windy passed along a soft start suggestion & I was going to put a time
> clock turning on from 10AM-2PM every day to utilize a fuller bank. I will
> look at the SOC option on the Radian, but it is 200+' away from the septic
> controller and conduit is in the ground.
> We have a HUP 2500 AHR/48-volt bank & 6,400 watt of PV tracked in a n-s
> canyon that limits the PV collection to 5 hours on a December day, that so
> far even running a 3/4 HP air compressor all day/every day-7 days a week
> has never dropped at night more than 5%.
>
> ----------------------------------------------------------------------------
> Dana Orzel Great Solar Works, Inc.
> 208.721.7003 dana at solarwork.com
> Idaho Contractor - # 028765 Idaho PV # 028374
> NABCEP # 051112-136 www.solarwork.biz
> "Responsible Technologies for Responsible People since 1988"
> ï Please consider the environment before printing this email.
>
>
> -----Original Message-----
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
> Behalf Of Chris Mason
> Sent: Friday, October 27, 2017 5:51 AM
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] Wattage 1/2 HP vs 1HP septic pumps
>
> What's the problem with the 1H pump you anticipate? We live on a 8KW
> Radian and it's very robust. We have load management relay system to
> handle the dryer, it's only allowed to work above 95% state of charge.
> Since your lift station has range, i.e., it doesn't have to work every
> minute of the day, you can control it so it works only during a SOC range
> or Time of Day range. You can also turn off other loads so there is enough
> power. If you run the lift pump during the night, there is less chance of
> a convection oven running at that time. Or mid morning when everyone is at
> work. Having time control or SOC control is very handy.
>
> On Wed, Oct 25, 2017 at 9:37 PM, Dana <dana at solarwork.com> wrote:
>
>> Ok all you whiz kids, bozos, & bolos:
>>
>>
>>
>> If I have a septic lift pump [off grid ouch] at 1HP/240 vac/8-amps to
>> meet all the usual state required overkill in septic design & a ½
>> HP/240 vac/4.9-amp pump would do the same job but it will take 10%
>> more time to dose 800 gallons.
>>
>> Powered by an 8 KW Outback Radian inverter.
>>
>> From a load point of view and a 240-volt 3 phase wild AC well pump
>> limiting the overall surge and general wattage is the smartest move,
>> but; Which pump will use less overall power? We are using 240 volt to
>> utilize both inverters and drop the load on either half of the Radian
>> inverter.
>>
>> Is there a smarter lift pump to use? ECM motor? Permanent magnet?
>>
>>
>>
>> ------------------------------------------------------------
>> ----------------
>>
>> Dana Orzel Great Solar Works, Inc.
>>
>> 208.721.7003 dana at solarwork.com
>>
>> Idaho Contractor - # 028765 Idaho PV # 028374
>>
>> NABCEP # 051112-136 www.solarwork.biz
>>
>> "Responsible Technologies for Responsible People since 1988"
>>
>> P Please consider the environment before printing this email.
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
> --
> Chris Mason
> NABCEP Certified Solar PV Installerâ¢
> Solar Design Engineer
> Generac Generators Industrial technician
>
> www.cometsolar.com <http://www.cometenergysystems.com>
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
More information about the RE-Wrenches