[RE-wrenches] System Monitor for HV Off Grid System?
Starlight Solar Power Systems
larry at starlightsolar.com
Fri Oct 20 19:08:04 EDT 2017
Right, it lacks many features. Old school method: tape a piece of paper next to the meter showing AH removed = xx % full. I think any shunt up to 1000 amps can be used. It can be programmed for different styles.
It also has two programmable relays to start a generator or notify the user to charge or whatever. For under $90 it has its place and covers the voltage range you need.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103
On Oct 20, 2017, at 3:38 PM, Sindelar Solar <Allan at sindelarsolar.com> wrote:
Larry,
Thank you for the referral to this item. Unless I'm missing something:
- it lacks the ability to provide % of full;
- it lacks a charge efficiency factor, and can thus develop an accumulated error;
- the accumulated error can be manually cleared but not automatically;
- it requires a separate 9-30VDC power supply, most likely a wall wart AC power supply;
- it looks as though it would work with a 100A/50mV shunt, but I'm not sure.
Am I correct about these?
Allan
On 10/20/2017 3:58 PM, Starlight Solar Power Systems wrote:
> Look at the JLD 404. 500Vdc, 10kA
> see http://www.evwest.com/catalog/product_info.php?products_id=162
>
> Larry Crutcher
> Starlight Solar Power Systems
>
> On Oct 20, 2017, at 2:48 PM, Sindelar Solar <Allan at sindelarsolar.com> wrote:
>
> Wrenches,
> I have an upcoming remote residential off grid upgrade job that uses one of the rare Michigan Energy Works inverter/charger/controller packages, this one from 1997, which the homeowner wants to continue using. The package uses a 120 volt nominal array (10 x BP90 in series) and a 144V nominal battery bank. I'm adding array (6 x 60-cell generic), replacing batteries (FLA with VRLA), and updating disconnects and overcurrent protection. Can anyone suggest a user-friendly system monitor that will work with this system voltage, something akin to a TriMetric 2020 or 2030? I can't think of one that will work with a system voltage this high. Mostly I'd like the percentage function for a nontechnical homeowner.
>
> Thank you, Allan
--
*Allan Sindelar*
allan at sindelarsolar.com <mailto:allan at sindelarsolar.com>
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list