[RE-wrenches] Panelboards in Series - Bus Ratings
Corey Shalanski
corey at joule-energy.com
Tue Oct 17 17:36:14 EDT 2017
*Scenario*
- 600A *dedicated PV* subpanel w/ (6) 100A circuit breakers, each
feeding a 60kW inverter (72.2A rated output)
- Subpanel is fused at 600A and connects to a larger main
distribution/combiner panel along with other similarly configured subpanels
*Question*
- Must the main panelboard be sized based on the combined total of OCPDs
protecting the subpanels, e.g. 600A + 600A + 600A + 600A = 2400A main panel
rating?
- Or can the main panelboard be sized based on the combined total of
inverter output ratings feeding the panel, e.g. 433.2A + 433.2A + 433.2A +
433.2A = 1732.8A main panel rating?
--
Corey Shalanski
Joule Energy
New Orleans, LA