[RE-wrenches] lithium batteries
Glenn Burt
glenn.burt at glbcc.com
Thu Oct 12 18:26:07 EDT 2017
The sonnen eco series of products were available before the PW2, and are available today through distributors.
They also take AC in and out, with batteries and inverter internal in a sleek enclosure. They are programmable for exporting restrictions.
-Glenn
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Darryl Thayer
Sent: Thursday, October 12, 2017 12:08 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] lithium battereis
Hello Jay and Larry.
As I mentioned I have had experience with only 3 systems, I have another one coming up. The charge controller problem has occurred in all of my systems, But this is perhaps a misunderstanding on my part. I used manufactures data, trying to attain maximum life. As mentioned by others, I would not install a system without BMS built in.
I am interested in powerwall-2 AC as it seems to have some advantage in no export, and the glamour of LI. I have not been able to get one, except through giving the project to a competitor. Does anyone else make a similar product? And does anyone have information on the actual product as far as pass-through and turn-down for no export systems?
Thanks to both of you and others for the information.
On Thu, Oct 12, 2017 at 10:40 AM, Starlight Solar Power Systems < larry at starlightsolar.com> wrote:
> Hello Darryl,
>
> Quote "You must be careful of LI because if you are floating, the
> voltage drops so little your CC will not necessarily pick-up.”
>
> We have sold hundreds of Li-ion batteries over the last 4 years. No
> one has had a problem with a PV solar charge controller or battery
> charger providing current when a load is applied. If the battery
> voltage is at equilibrium with the charger, float mode and current
> basically zero, the slightest load will be directed to the charge
> source as it attempts to maintain voltage.
>
> Hey Jay,
>
> We sell Relion with cylindrical cells and prismatic cells from Elite
> Power Solutions (GBS) and LiFeBlue Battery. We have never had a cell
> failure with any battery yet so as for cell quality, all brands are
> working well. The problems we have had are always with the EMS systems.
>
> My thoughts comparing the two battery types are one type has fewer
> points of failure. In a 100AH 12 volt pack using cylindrical cells,
> you have many dozens of batteries and connections compared to 4 to 16
> prismatic cells. I know Tesla cars have worked extremely well with
> 7000+ cylindrical cells but he has spent millions making it work. In
> the Li battery market we are involved with, I’m not so sure the
> manufacturers have provided the same level of QC.
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
> On Oct 7, 2017, at 8:05 PM, Darryl Thayer <darylsolar1 at gmail.com> wrote:
>
> I have only limited experience with Lithium batteries. But in that
> experience, a module of small cylindrical cells will have a higher
> power, faster charge, and discharge. For the same chemistry, the
> prism cells will have a little higher energy density. For long cycle
> life and slow aging, the differences in battery additives meaning the
> manufacturer are paramount. In using Li-ion there are a few tricks.
> The voltage is very stable, so you can not use voltage for the state
> of charge. For LA you will float 13.4 forever, then when you draw
> power, the voltage drops. even at low draw, the voltage drops to the
> 12.6 range. You must be careful of LI because if you are floating,
> the voltage drops so little your CC will not necessarily pick-up.
> Some manufacturers give you instruction via mod bus or some form of
> communication. So ask your CC supplier and your battery people good luck some do not even understand their own equipment.
>
> On Sat, Oct 7, 2017 at 10:16 AM, jay <jay.peltz at gmail.com> wrote:
>
> > To follow along with the lithium questions,
> >
> > I’m wondering what thoughts/information people have on prismatic vs
> > cylindrical lithium family batteries?
> >
> > My questions are quality,cycle life, pros/cons,recycling?
> >
> > Thanks
> >
> > jay
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list