[RE-wrenches] Sunny Island grid tie battery back and backup stability issues with ABB
Jerry Shafer
jerrysgarage01 at gmail.com
Mon Sep 18 22:14:46 EDT 2017
Luminalt
As l recall the SI will move the freq around to regulate the SMA inverter,
not having a SMA it may be attempting to force the inverter down. You can
widen the freq programming on the ABB inverter to prevent the shut down but
this will not prevent the volts from bouncing around, you may want to
adjust the inverter AC volts to get past the wave.. FYI, SMA will shortly
have a replacement for the SI thats 240 vac and alot smarter too.
Jerry
On Sep 18, 2017 1:26 PM, "Peter Giroux" <pgiroux at mindspring.com> wrote:
> August
>
> We had something similar happen a few years ago on an AC coupled
> application using a 5048 Sunny Island ( with transformer ) and a Sunny Boy
> 7000. In a grid down scenario the Sunny boy dropped off line. After a few
> calls with SMA sharing the error codes it turned out the Sunny Island was
> not delivering 60 hertz, not even 59, so we had to reprogram the Sunny Boy
> to recognize and run on 57 hertz.
>
> SMA was gracious enough to share the "magic code " and walk me through
> the programming. Once the Sunny Boy was reset to operate on the lower hertz
> range everything worked great. You may have a similar situation, not sure
> if the ABB folks will help with the hertz adjustment but you should give it
> a try before springing for a sunny boy.
>
> Peter Giroux
> ASAE
>
> ----- Original Message -----
> *From:* August Goers <august at luminalt.com>
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Sent:* Monday, September 18, 2017 5:48 PM
> *Subject:* [RE-wrenches] Sunny Island grid tie battery back and backup
> stability issues with ABB
>
> Hi Wrenches -
>
> We have an ~3 year old grid tied battery backup system with a SMA Sunny
> Island 4548 and Power-One (now ABB) PVI-5000 inverter. There is also an
> Outback PSX-240 to boost the Sunny Island voltage to 240 volts.
>
> We recently returned to the site for an annual service call and tested the
> system by simulating a power outage. The Sunny Island kicked in just fine
> and provided stable voltage for the backup loads. However, the ABB tries to
> connect and immediately we see that voltage and frequency of the Sunny
> Island grid start to rapidly fluctuate. I have a feeling that my Fluke
> meter is not capturing the fluctuations properly, but I was seeing voltage
> fluctuate in the 238 to 242 volt range and frequency rapidly fluctuate
> between 59 and 61 Hz.
>
> The ABB connects for a minute or two and then gives us a grid out of range
> error. This occurs when we have lots of irradiance and also under
> relatively low light conditions. I've already been on the phone with SMA
> tech support several times and verified that all the Sunny Island settings
> are good.
>
> Has anyone else seen this type of instability issue and did you find a
> fix? We might need to install a Sunny Boy.
>
>
> Thanks,
>
> August
>
> *August Goers*
>
> Luminalt
>
>
>
>
> ------------------------------
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170918/d674b22d/attachment.htm>
More information about the RE-Wrenches
mailing list