[RE-wrenches] Hurricane damage to solar arrays
Jason Szumlanski
jason at floridasolardesigngroup.com
Fri Sep 15 09:54:50 EDT 2017
5400pa I believe in all cases.
I don't see any evidence of flying debris causing damage at all so far.
Every damaged module that remained in place is explained by another module
hitting it.
On Thu, Sep 14, 2017 at 11:38 PM, Ray <ray at solarray.com> wrote:
> What was the pressure rating for the modules that got sucked off the
> racks? Also, is it possible that flying debris caused some of the random
> location module failures?
>
> Ray Walters
>
> Remote Solar
>
> On 9/14/17 1:53 PM, Jason Szumlanski wrote:
>
> More early anecdotal data...
>
> We are finding NO anchors pulled out of roofs, regardless of roof type or
> attachment type. That is clearly not the failure point. We also see no
> attachment to L-foot or L-foot to rail issues. And contrary to my
> expectation, we see no t-bolt failures. What's happening? The panels
> themselves are flexing (bowing) sufficiently to work their way right out of
> the mid-clamps. This applies both to Unirac's older 1-inch space clamps and
> newer 1/4 inch bonding mid-clamps.
>
> This attached pictured system had panels on a north roof pitched very
> slightly to the south. We had northeast hurricane winds in this area, and
> the way the wind went under these panels was obviously what caused the
> panels themselves to fail. This is an essentially flat roof commercial
> application. It was bad luck to have the wind direction from the northeast
> corner (the NW edge of the eye wall passed right over this area). But we
> are seeing similar results on residential pitched hip and gable roofs in
> terms of the failure mode.
>
> What's interesting is that there is no rhyme or reason to where in the
> array we see damage. I have seen absolutely no catastrophic damage on a
> residential roof - just one or 2 modules mostly. And the missing module can
> be on the lower edge, upper edge, or right in the middle of the array. More
> often than not, the t-bolt and mid-clamp assembly is still sitting right
> there in the channel of the Unirac Solarmount rail, but a module is
> missing. It's quite freaky.
>
> And much like tornado damage I have seen on TV, houses adjacent to each
> other have very different fates. We have a new community (100+ homes slated
> for solar) with about two dozen homes completed, and just one home had a
> panel pop out in the middle of an array. It was gently deposited onto the
> adjacent panel with absolutely no damage and the DC leads still connected
> to the microinverter.
>
> One issue we are facing is that when panels fly off, something has to give
> with the DC leads to microinverters. No panel leads have been broken so
> far. In most cases, the MC4 connectors simple un-snap somehow - no loss of
> crimped connectors. We have a few cases of leads ripped out of the
> microinverter case completely. The microinverter bracket is badly bent on
> many microinverters, indicating that there was tremendous force until
> something gave up. I am extremely hesitant to reuse these microinverters
> because the force on the DC input leads must have been huge. I think we are
> going to insist on microinverter replacement when replacing modules in
> these cases.
>
> Hopefully I will have more, but not too much more to come. It looks like
> we did very well here (as an industry). There are spotty issues, but it's
> far from the catastrophe that kept me up for multiple nights before and
> after Irma. Then again, many people have not returned home yet.
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
>
> On Wed, Sep 13, 2017 at 6:18 PM, Jason Szumlanski <jason@
> floridasolardesigngroup.com> wrote:
>
>> [image: Inline image 1]
>> I'm based in Fort Myers and we cover the hardest hit areas from Irma. We
>> are in the "stuff" right now, so I'll make this brief until I have more
>> time, which might be a while. We are seeing quite a bit of minor damage and
>> some major damage. We're getting calls from all dealers' customers and a
>> couple of our own clients. We have several homes with one or two panels
>> dislodged. There is no rhyme or reason. Some are middle of arrays, some on
>> edges. Panels are ripped right off rails, leads ripped from microinverters.
>> Strangely, it looks like the panel j-box connection and MC4 connectors
>> survived better than the microinverter end of the DC leads. Amazingly, we
>> have several panels that were blown onto driveways, other roofs, and pool
>> cages with NO DAMAGE except frame scrapes. Very weird. We haven't seen a
>> shattered panel yet, but it's early.
>>
>> I'm heading to a self-storage facility tomorrow where there are three
>> 25kw systems on different buildings. Two buildings are unscathed. One
>> building lost ALL of the panels apparently. Tornado? Hard to say.
>>
>> So far (other than the 25kw I have not evaluated) we have not seen a
>> single fastener pulled out. All of the failures are panel top and mid
>> clamps at this time. Anchor and rails remain intact. Possibly installation
>> errors? Possibly sheared off T-bolts? Hard to tell and we may never fully
>> know.
>>
>> We generally require 48 inch spacing between anchors into trusses for
>> engineered systems. The pullout values are pretty high. It looks like the
>> attachment points into the roof are not going to be the failure point in
>> the systems in Florida, but there is a LOT of work to be done still. It's
>> going to be a very interesting few months ahead!
>>
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>>
>>
>> On Tue, Sep 12, 2017 at 3:09 PM, James Rudolph <jamesrudolph99 at gmail.com>
>> wrote:
>>
>>> Aloha Everyone,
>>> I was just wondering how all the PV arrays did during these storms?
>>> Does Florida have higher pull out values and wind designs for their
>>> PV/H20 systems?
>>> Is there any thing the rest of us could learn from all this?
>>> Photos?
>>>
>>>
>>> Mahalo Nui Loa,
>>>
>>>
>>> *James B. Rudolph*
>>>
>>> *Hawaii Unified*
>>>
>>> *Director of Energy*
>>>
>>> *ES Electrician # 10816*
>>>
>>> *NABCEP Certified PV Installer # 091209-155*
>>>
>>> *80*
>>>
>>>
>>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <https://mailtrack.io/trace/link/6bdbef9da91352bff26de94c5dc72965048348d4?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=5f24cc89f2e95bff>
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <https://mailtrack.io/trace/link/7b9d2b1867c9adbd52fe13ac197b421b4beeec2b?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=0e0fd18c0c5e37ae>
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm <https://mailtrack.io/trace/link/6582d7bb4520a8e73e3ee03dc8faca413529bfaa?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=55e2381aa989b7d6>
>
> Check out or update participant bios:www.members.re-wrenches.org <https://mailtrack.io/trace/link/401b770a411b36837d1963ad0ebb98ec71ab4283?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=56fc5e4a91866dea>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/6bdbef9da91352bff26de94c5dc72965048348d4?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=5f24cc89f2e95bff>
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
> <https://mailtrack.io/trace/link/7b9d2b1867c9adbd52fe13ac197b421b4beeec2b?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=0e0fd18c0c5e37ae>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/6582d7bb4520a8e73e3ee03dc8faca413529bfaa?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=55e2381aa989b7d6>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/401b770a411b36837d1963ad0ebb98ec71ab4283?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=56fc5e4a91866dea>
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170915/13724cf5/attachment.htm>