[RE-wrenches] AC Coupled Enphase
bob at midnitesolar.com
bob at midnitesolar.com
Wed Aug 30 18:13:58 EDT 2017
On 8/30/2017 5:54 AM, Drake wrote:
> Hi boB,
>
> Would there be any issues with delayed control of the microinverters?
> We do plan to use disconnects for maintenance.
>
> Thanks,
>
> Drake
>
I highly doubt there would be enough delay to worry about anything
regarding battery damage....
Even with Rule 21 or its cousins in a normal home installation.
boB
> At 06:27 PM 8/29/2017, you wrote:
>> Content-Type: multipart/alternative;
>> Â boundary="------------155C815B9802686293824DDD"
>> Content-Language: en-US
>>
>>
>> SSRs, especially AC SSRs made from thyrisotrs (scrs and/or triacs)Â
>> are "leaky" in general
>>
>> so when turned OFF, can cause a shock.... Maybe not enough to kill
>> you but maybe enough
>>
>> to make you fall off the roof !
>>
>> I'm not sure why the disconnects aren't good enough which should
>> already be in place ?
>>
>> boB
>>
>> On 8/29/2017 4:53 AM, Jason Szumlanski wrote:
>>> My vote would still be to use two single pole relays as suggested
>>> previously to kill each leg. That way you build in redundancy and
>>> dropping either leg will do the trick. In fact, it sounds like this
>>> would be even better than a two pole relay for the redundancy reason.
>>>
>>> The other factor is whether you are using NO or NC relays. My
>>> engineer requires NO relays in these cases so they would fail in the
>>> open position only. I'm not sure how this would work, or if it would
>>> work with solid state relays. I have never dug into this. My
>>> understanding is that solid state relays fail in the closed
>>> condition (shorted). This would preclude their use in a situation
>>> where opening the circuit is the preferred failure mode. Maybe
>>> someone with some more knowledge in this area can chime in on
>>> whether SSRs are a good idea in this scenario.
>>>
>>> Jason Szumlanski
>>>
>>>
>>> On Mon, Aug 28, 2017 at 10:19 PM, Nick Soleil
>>> <nsoleil at enphaseenergy.com <mailto:nsoleil at enphaseenergy.com>> wrote:
>>>
>>> The one-pole relay will work for de-energizing any of the
>>> Enphase microinverters.
>>>
>>> Nick Soleil
>>> Field Application Engineer
>>> Enphase Energy
>>> Cell: 707-321-2937 <tel:%28707%29%20321-2937>
>>>
>>> On Aug 28, 2017, at 6:03 PM, Drake
>>> <drake.chamberlin at redwoodalliance.org
>>> <mailto:drake.chamberlin at redwoodalliance.org>> wrote:
>>>
>>>> Hi Nick,
>>>>
>>>> I should mention that the inverters being AC coupled are
>>>> M-250s, not the new IQ series. Would that make any difference?
>>>>
>>>> Thanks,
>>>>
>>>>
>>>> Drake
>>>>
>>>>
>>>> At 03:12 PM 8/28/2017, Drake wrote:
>>>>> Hi Nick,
>>>>>
>>>>>
>>>>> At 11:20 AM 8/28/2017, you wrote:
>>>>>> Content-Language: en-US
>>>>>> Content-Type: multipart/alternative;
>>>>>> Â Â Â Â Â Â Â Â
>>>>>> boundary="_000_56449940CA694DDAABB811FCC45A2070enphaseenergycom_"
>>>>>>
>>>>>> You can use a one-pole relay. We show one-pole
>>>>>> switching in our zero-export, self-consumption
>>>>>> doc for PEL applications.
>>>>>>
>>>>>> Nick Soleil
>>>>>> Field Application Engineer
>>>>>> Enphase Energy
>>>>>> Cell: 707-321-2937 <tel:%28707%29%20321-2937>
>>>>>>
>>>>>> On Aug 28, 2017, at 6:44 AM, Drake
>>>>>> <drake.chamberlin at redwoodalliance.org
>>>>>> <mailto:drake.chamberlin at redwoodalliance.org>> wrote:
>>>>>>
>>>>>>> Hello Wrenches,
>>>>>>>
>>>>>>> I am going to AC couple some Enphase
>>>>>>> inverters and found some really nice solid
>>>>>>> state, single pole relays to control them
>>>>>>> with. Enphase says I must use 2 pole relays
>>>>>>> for the control current even though the
>>>>>>> disconnects will turn off all power for
>>>>>>> maintenance.
>>>>>>>
>>>>>>> Enphase claims that the inverters will not
>>>>>>> shut down reliably with only one line
>>>>>>> opened. This does not make sense to me in
>>>>>>> view of UL 1741. Is Enphase correct in their
>>>>>>> claim, or are there other reasons that both
>>>>>>> poles need to be opened
>>>>>>>
>>>>>>> I want to use the solid state relays because
>>>>>>> the coil voltage is between 3 and 32 volts.
>>>>>>> This would avoid the need to add voltage
>>>>>>> dropping series resistors to protect the
>>>>>>> coil for higher battery voltages.
>>>>>>>
>>>>>>> Alternatively, does anyone know of
>>>>>>> reasonably priced, 2 pole solid state relays?
>>>>>>>
>>>>>>> Thanks,
>>>>>>>
>>>>>>> Drake
>>>>>>>
>>>>>>> Â
>>>>>>> Drake Chamberlin
>>>>>>> Athens Electric LLC
>>>>>>> OH License 44810
>>>>>>> CO License 3773
>>>>>>> NABCEP Certified Solar PV
>>>>>>> 740-448-7328 <tel:%28740%29%20448-7328>
>>>>>>>
>>>>>>> _______________________________________________
>>>>>>> List sponsored by Redwood Alliance
>>>>>>>
>>>>>>> List Address:
>>>>>>> RE-wrenches at lists.re-wrenches.org
>>>>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>>
>>>>>>> Change listserver email address & settings:
>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>> <https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>
>>>>>>>
>>>>>>>
>>>>>>> List-Archive:
>>>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>>> <https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>
>>>>>>>
>>>>>>>
>>>>>>> List rules & etiquette:
>>>>>>> www.re-wrenches.org/etiquette.htm
>>>>>>> <https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>
>>>>>>>
>>>>>>> Check out or update participant bios:
>>>>>>> www.members.re-wrenches.org
>>>>>>> <https://mailtrack.io/trace/link/42b8962882456a240060cea7f870a550cf549bc6?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=8682c7a34db623bd>
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>
>>>>>>
>>>>>>
>>>>>> List-Archive:
>>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>> <https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>
>>>>>>
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> www.re-wrenches.org/etiquette.htm
>>>>>> <https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> www.members.re-wrenches.org
>>>>>> <https://mailtrack.io/trace/link/9b840d0d9b3573fe10be9ca23650f9910436d5fb?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&userId=1613865&signature=125e41a41f5138ad>
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> <https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>
>>>>>
>>>>>
>>>>> List-Archive:
>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>> <https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>
>>>>>
>>>>>
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>> <https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>
>>>>>
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>>> <https://mailtrack.io/trace/link/9b840d0d9b3573fe10be9ca23650f9910436d5fb?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&userId=1613865&signature=125e41a41f5138ad>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> <https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>
>>>>
>>>>
>>>> List-Archive:
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>> <https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>
>>>>
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> <https://mailtrack.io/trace/link/e5dd443e106ab9262a64531e245e33cacc6439c3?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1ff02acb7afaa5ce>
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> <https://mailtrack.io/trace/link/df1a46cc62f80e77abb320b6b58d2daa1df33313?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=5658938ab50f2b2d>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/d637b44281f438904170f585d45de0c029d858d0?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4e891bb2cdab5fbc>
>>>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> <https://mailtrack.io/trace/link/e6c3b50ab784871396cf8aa61952a354fd078c8c?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=5c6459243bdea642>
>>>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/e5dd443e106ab9262a64531e245e33cacc6439c3?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1ff02acb7afaa5ce>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/df1a46cc62f80e77abb320b6b58d2daa1df33313?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=5658938ab50f2b2d>
>>>
>>>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address:
>>> RE-wrenches at lists.re-wrenches.org
>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <http://www.re-wrenches.org/etiquette.htm>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170830/fc14b27f/attachment.htm>
More information about the RE-Wrenches
mailing list