[RE-wrenches] anything like Generac Smart Management Module for a solar critical backup panel

Chris Mason cometenergysystems at gmail.com
Wed Aug 30 07:11:12 EDT 2017


Can you read the load from the inverter? On the Outback systems you can
read the API from the MATE3 via ethernet/JSON string.

On Tue, Aug 29, 2017 at 5:37 PM, Howard Arey <scot.arey at solarcentex.com>
wrote:

> Not SOC issue but rather a peak inverter output issue: 5,000 watts con and
> 6,600 surge for 10 seconds (I believe the latter is right number). That is
> the constraint I’m trying to live under.
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Chris Mason
> *Sent:* Tuesday, August 29, 2017 4:34 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] anything like Generac Smart Management
> Module for a solar critical backup panel
>
>
>
> If there is an API from which you can determine SOC, you how to do load
> management with a Raspberry Pi. I can help with that if you want.
>
>
>
> On Tue, Aug 29, 2017 at 3:55 PM, Howard Arey <scot.arey at solarcentex.com>
> wrote:
>
> Hello again, wrenches.
>
>
>
> I know many of us have run into the quandary and that is  prioritizing
> loads in a critical load panel.
>
>
>
> About to put in some LG RESU units with the SE7600 StorEdge and the 21
> amps continuous is pretty tough.
>
>
>
> But with some smart, automated load management, this can work just fine.
>
>
>
> Is there anything like the Generac SMM (http://www.generac.com/all-
> products/transfer-switches/home-backup) out there that does not depend on
> decreasing cycles/hz to recognize its bumping into max load conditions?
>
>
>
> *Howard “Scot” Arey*
>
> 254-300-1228 <(254)%20300-1228>
>
> scot.arey at solarcentex.com
>
>
>
> [image: Solar Centex Logo - No Back.png 10 percent resize]
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
>
>
> --
>
> Chris Mason
>
> NABCEP Certified Solar PV Installer™
>
> Solar Design Engineer
>
> Generac Generators Industrial technician
>
>
>
> www.cometsolar.com <http://www.cometenergysystems.com>
>
> 264.235.5670 <(264)%20235-5670>
>
> 869.662.5670 <(869)%20662-5670>
>
> Skype: netconcepts
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170830/a4a776c9/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 51135 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170830/a4a776c9/attachment.png>


More information about the RE-Wrenches mailing list