SSRs, especially AC SSRs made from thyrisotrs (scrs and/or triacs) are
"leaky" in general
so when turned OFF, can cause a shock.... Maybe not enough to kill you
but maybe enough
to make you fall off the roof !
I'm not sure why the disconnects aren't good enough which should already
be in place ?
boB
On 8/29/2017 4:53 AM, Jason Szumlanski wrote:
> My vote would still be to use two single pole relays as suggested
> previously to kill each leg. That way you build in redundancy and
> dropping either leg will do the trick. In fact, it sounds like this
> would be even better than a two pole relay for the redundancy reason.
>
> The other factor is whether you are using NO or NC relays. My engineer
> requires NO relays in these cases so they would fail in the open
> position only. I'm not sure how this would work, or if it would work
> with solid state relays. I have never dug into this. My understanding
> is that solid state relays fail in the closed condition (shorted).
> This would preclude their use in a situation where opening the circuit
> is the preferred failure mode. Maybe someone with some more knowledge
> in this area can chime in on whether SSRs are a good idea in this
> scenario.
>
> Jason Szumlanski
>
>
> On Mon, Aug 28, 2017 at 10:19 PM, Nick Soleil
> <nsoleil at enphaseenergy.com <mailto:nsoleil at enphaseenergy.com>> wrote:
>
> The one-pole relay will work for de-energizing any of the Enphase
> microinverters.
>
> Nick Soleil
> Field Application Engineer
> Enphase Energy
> Cell: 707-321-2937 <tel:%28707%29%20321-2937>
>
> On Aug 28, 2017, at 6:03 PM, Drake
> <drake.chamberlin at redwoodalliance.org
> <mailto:drake.chamberlin at redwoodalliance.org>> wrote:
>
>> Hi Nick,
>>
>> I should mention that the inverters being AC coupled are M-250s,
>> not the new IQ series. Would that make any difference?
>>
>> Thanks,
>>
>>
>> Drake
>>
>>
>> At 03:12 PM 8/28/2017, Drake wrote:
>>> Hi Nick,
>>>
>>>
>>> At 11:20 AM 8/28/2017, you wrote:
>>>> Content-Language: en-US
>>>> Content-Type: multipart/alternative;
>>>>
>>>> boundary="_000_56449940CA694DDAABB811FCC45A2070enphaseenergycom_"
>>>>
>>>> You can use a one-pole relay. We show one-pole switching in
>>>> our zero-export, self-consumption doc for PEL applications.
>>>>
>>>> Nick Soleil
>>>> Field Application Engineer
>>>> Enphase Energy
>>>> Cell: 707-321-2937 <tel:%28707%29%20321-2937>
>>>>
>>>> On Aug 28, 2017, at 6:44 AM, Drake
>>>> <drake.chamberlin at redwoodalliance.org
>>>> <mailto:drake.chamberlin at redwoodalliance.org>> wrote:
>>>>
>>>>> Hello Wrenches,
>>>>>
>>>>> I am going to AC couple some Enphase inverters and found some
>>>>> really nice solid state, single pole relays to control them
>>>>> with. Enphase says I must use 2 pole relays for the control
>>>>> current even though the disconnects will turn off all power
>>>>> for maintenance.
>>>>>
>>>>> Enphase claims that the inverters will not shut down reliably
>>>>> with only one line opened. This does not make sense to me in
>>>>> view of UL 1741. Is Enphase correct in their claim, or are
>>>>> there other reasons that both poles need to be opened
>>>>>
>>>>> I want to use the solid state relays because the coil voltage
>>>>> is between 3 and 32 volts. This would avoid the need to add
>>>>> voltage dropping series resistors to protect the coil for
>>>>> higher battery voltages.
>>>>>
>>>>> Alternatively, does anyone know of reasonably priced, 2 pole
>>>>> solid state relays?
>>>>>
>>>>> Thanks,
>>>>>
>>>>> Drake
>>>>>
>>>>>
>>>>> Drake Chamberlin
>>>>> /Athens Electric LLC
>>>>> OH License 44810
>>>>> CO License 3773
>>>>> NABCEP Certified Solar PV
>>>>> 740-448-7328 <tel:%28740%29%20448-7328>
>>>>>
>>>>> /_______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> <https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>
>>>>>
>>>>>
>>>>> List-Archive:
>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>> <https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>
>>>>>
>>>>>
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>> <https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>
>>>>>
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>>> <https://mailtrack.io/trace/link/42b8962882456a240060cea7f870a550cf549bc6?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=8682c7a34db623bd>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> <https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>
>>>>
>>>>
>>>> List-Archive:
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>> <https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>
>>>>
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> <https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> <https://mailtrack.io/trace/link/9b840d0d9b3573fe10be9ca23650f9910436d5fb?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&userId=1613865&signature=125e41a41f5138ad>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>
>>>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> <https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>
>>>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/9b840d0d9b3573fe10be9ca23650f9910436d5fb?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&userId=1613865&signature=125e41a41f5138ad>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> <https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/e5dd443e106ab9262a64531e245e33cacc6439c3?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1ff02acb7afaa5ce>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/df1a46cc62f80e77abb320b6b58d2daa1df33313?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=5658938ab50f2b2d>
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/d637b44281f438904170f585d45de0c029d858d0?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4e891bb2cdab5fbc>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://mailtrack.io/trace/link/e6c3b50ab784871396cf8aa61952a354fd078c8c?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=5c6459243bdea642>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/e5dd443e106ab9262a64531e245e33cacc6439c3?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1ff02acb7afaa5ce>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/df1a46cc62f80e77abb320b6b58d2daa1df33313?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=5658938ab50f2b2d>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170829/a6f98d38/attachment.htm>
More information about the RE-Wrenches
mailing list