[RE-wrenches] Over voltage error message

Dave Angelini Offgrid Solar offgridsolar at sti.net
Fri Jul 21 10:43:55 EDT 2017


I remember beta testing with Schneider in 2006 and the effect was there
but quickly went away with networked charge sources. --Dave


> Wrenches...
>
> At my former employer this same thing actually occurred with their
> controllers about 7-9 years ago... caused a bit of a stink back then until
> we did some research on the phenomenon.   Jay was correct in that the
> right
> circumstances need to line up for the customer and most metering even see
> this with the way products  are sampling.
>
> This is also combined with an effect called "Coup De Fouet"  or whip
> effect. There are a lot of articles about the loading of a battery how the
> battery voltage acts like the end of a whip, when you look at the DC
> voltage over time on a scope.   This can occur in the reverse at the end
> of
> the charge with the right circumstances.
>
> When batteries are charging and they are near their peak and you attempt
> to
> remove the charge, especially if there is no or very little load on the
> batteries and you try to stop charging, the chemical reaction within the
> battery is still occurring even without the source coming from the
> controller.  It takes some time 3-4 mins with no load for the chemical
> reaction to slow down,  during this time you can see a voltage surge, with
> some of the testing we did we saw as high as 8-10 volts jump for 30-180
> seconds...  If the controller or monitoring device "samples" the voltage
> at
> this time you are going to get bad voltage reading.
>
>
>
>
>
>
> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
> Steve Higgins
> Technical Services Manager
> m +1.206.790.5840
> f +1.902.597.8447  *e* steve at surrette.com
> <#UNIQUE_ID_SafeHtmlFilter_> <http://www.facebook.com/RollsBattery>
> <http://www.facebook.com/RollsBattery>
> <http://www.twitter.com/RollsBattery>
> <https://www.youtube.com/user/RollsBattery>
> <https://www.linkedin.com/company/rolls-battery-engineering>
> <http://www.instagram.com/RollsBattery>
> <http://www.instagram.com/RollsBattery>
> <http://www.instagram.com/RollsBattery>
> ------------------------------
> CONFIDENTIALITY: The information transmitted herein is intended only for
> the addressee and may contain confidential, proprietary and/or privileged
> material. Any unauthorized review, distribution or other use of or the
> taking of any action in reliance upon this information is prohibited. If
> you receive this email in error, please contact the sender and delete or
> destroy this message and all copies.
> ------------------------------
>
> On Tue, Jul 18, 2017 at 5:25 PM, Jerry Shafer <jerrysgarage01 at gmail.com>
> wrote:
>
>> Wrenches
>> The Outback system with grid connection would be programmed for grid
>> connection all the way from the inverter to the Outback FM CC, using a
>> midnite CC this option may not be possible resulting to a CC push if the
>> grid disconnects resulting in a spike. the disconnect might be from
>> settings to tight or as it was said utility spikes. You might thing that
>> the battery bank should take it up but internal resistance in the
>> battery
>> or to it may prevent it. The other thing I would look at is connections,
>> if
>> there is any resistance in a connection this could happen.
>>
>> On Mon, Jul 17, 2017 at 2:36 AM, Drake <drake.chamberlin@
>> redwoodalliance.org> wrote:
>>
>>> Hello Wrenches,
>>>
>>> My client reported seeing an overvoltage error message on her Mate 3 on
>>> a
>>> Radian system. The Radian is selling to the grid and is being fed by a
>>> Midnite Classic 200. It has shown two spikes so far, the last one going
>>> to
>>> 67 volts and lasting 1 second. The batteries are Concorde AGM, 305 AH.
>>>
>>> Does this momentary spike seem like a problem or a warning of problems
>>> to
>>> come?
>>>
>>> Thanks,
>>>
>>> Drake
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: http://www.mail-archive.com/re
>>> -wrenches at lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridsolar at sti.net
text 209 813 0060



More information about the RE-Wrenches mailing list