[RE-wrenches] Xantrex XW 6048A unregulated during charging

Dave Angelini Offgrid Solar offgridsolar at sti.net
Thu May 4 10:03:46 EDT 2017


I would add that after loading firmware on Outback or Schneider there
sometimes have been cases where it showed the new firmware but it was
still running the old.
The solution was to choose original factory default firmware. After that
the unit would load the latest firmware that you had previously installed.
Now that is maddening.  There are so many XW's and Outbacks out there that
I am surprised at how well they run. I am not a big fan of loading new
firmware unless you have to.Most of this gear is fine with what it had
offgrid. Leave it alone unless you know exactly why you are changing. The
firmware has release notes and you should read them. The combox has recent
firmware that stopped the "bricking " issue it had. I would do that one
for sure! I like the config tool also along with combox.


> As with anything these days I would make damn sure that the firmware OF
> ALL components in the system have been updated w/ the latest firmware
> prior to changing anything. I personally am not a big fan of the com box
> and I have the “Con fig” tool and I find after the learning curve its
> the best method of addressing info & updating. Mis matched firmware seems
> to be the # 1 issue w/ all the manufactures today. Tump
>> On May 3, 2017, at 6:17 PM, Jason Lerner <wapalco at rockisland.com> wrote:
>>
>> Hello All,
>>
>> I’m working on a system with 3 Xantrex XW 6048’s that has grid on
>> AC1 and a 20 kw generator on AC2.  When charging from grid it regulates
>> during an absorption charge at 58.2 where it should.  When charging from
>> AC 2 - generator, the battery Voltage rises above 62 VDC,  but not every
>> single time.  All the settings are correct, EQ is turned off, and if it
>> accidentally got turned on is set at the same Voltage as the absorption
>> setting.  Customer has a brand new 33 kWh AGM battery bank,  that I
>> would rather not fry.  This is a battery backup system with no PV.
>>
>> I have checked all the temperature sensors (they seem good) and tried
>> charging with them plugged in,  and with them unplugged and it doesn’t
>> seem to change the situation.
>>
>> Has anybody else seen this happen before?  Any suggestions?
>>
>> Thanks very much,
>>
>> Jason Lerner
>> Waldron Power and Light Co.
>> (888) 927-2526
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
>> Tump at swnl.net
>> <blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net>
>>               www.SWNL.net
>> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>>                 Solarwinds Northernlights
>>        Serving Mid Coast Maine & Northern California
>>                          207-832-7574   Cl. 610-517-8401
>>                               Blair "TUMP" May
>>                ********  MAINE'S CHARTER ********
>>                       NABCEP    "Certified PV Installer"
>>
>>               ********  MAINE'S CHARTER ********
>>                   Trace Xantrex "Certified" Dealer / Installer"
>>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridsolar at sti.net
text 209 813 0060



More information about the RE-Wrenches mailing list