[RE-wrenches] Third Radian ---> Class T Fuse With/Without Fuse Holder
Tump
tump at swnl.net
Fri Apr 28 08:08:09 EDT 2017
I have seen these conduit boxes torch off, like to see and have in free air. Supporting battery cable makes more sense then the hassle of installing this is a LB.
T
> On Apr 27, 2017, at 7:41 PM, Jerry Shafer <jerrysgarage01 at gmail.com> wrote:
>
> Wrenches
> In the event you or some else installed a Class T fuse and you want to protect it a little more from cable stress, installing it inside a PVC C conduit body and cover and fastening the cables to the fuse inside that, this will protect the fuse from stress and metallic contact and you can put a label on it stating size and type.
> Jerry
>
> On Wed, Apr 26, 2017 at 6:05 PM, Matthew Sirum <matthewsirum at gmail.com <mailto:matthewsirum at gmail.com>> wrote:
> Greetings William,
>
> Good point. This is something I always take into consideration. I
> have used Class T Fuses in many situations with and without their fuse
> holders. In the case of the installation shown in my custom DC Bus
> System pictures the wire/cable type and wire management avoid putting
> too much physical stress on the Class T Fuses. The #4 AWG conductors
> are supported from above and apply very little stress on the fuses
> they connect to. The 4/0 AWG cabling is Cobra X-Flex (fine stand,
> very flexible) and each of these conductors is secured a few inches
> from where they connect to their fuses. Care was taken in making up
> these connection and they were all carefully adjusted and inspected to
> ensure they would not stress the fuses. I feel really good about how
> it all came together. The same care and attention will be needed
> whenever these connections are serviced and the fasteners are
> torqued/tightened. When well planned and carefully assembled I do not
> have concern there will be any issues related to not using the fuse
> holder. I also think about this another way as well... Using the
> Class T Fuse Holder adds another 2 connections to the circuit. I try
> to remind myself that more connections can equal more chance of
> issues... Although, if a manufacturer of a Class T Fuse states the
> fuse holder must be used with their fuse there could be an NEC
> violation by not using it.
>
> One thing to note about the use of these fuses in this installation is
> that they are supplemental over current protection (OCP). Each
> positive (ungrounded) conductor connecting to this DC Bus System has a
> means of primary over current protection and disconnect on its
> opposite end. The battery systems, the charge controllers, and the
> inverter/chargers all have circuit breaker disconnects on their
> respective positive circuit conductors connecting to this DC Bus
> System. I have seen other folks build without having the needed
> appropriate means of disconnect and OCP; although most folk are
> probably more likely to include the primary OCP, but not consider the
> supplemental OCP. The supplemental OCP (Class T Fuses) provide
> protection in the event of a fault or short in a circuit between the
> Bus System and the other OCP at the other equipment.
>
> Like many folks I have installed and worked on battery systems where
> we install a Class T Fuse directly onto the positive terminal of the
> battery bank or via some form of busbar or connector etc. In these
> cases not only do we need to take care not to stress the fuse, but the
> fuse itself (and added busbar/connector etc) can act like a lever and
> along with the mating cable lug(s) create too much stress on the
> battery terminal... Potentially damaging the terminal, the inner
> battery connection to the terminal, and/or the seal between the
> battery case and the terminal. Carelessly tightening the
> hardware/fasteners to assemble these items to the battery terminal is
> a common way of inflicting damage on the battery as well. I know I
> have been involved in some service situations where there was more
> stress on the Class T Fuse than I would like to see, but as best I
> know there have not been any fuse failures because of it.
>
> Thanks for bringing up this question!
>
> Best regards,
>
> ----MATT
>
> Matthew Sirum
> P.O. Box 1227
> Greenfield, MA 01302-1227 USA
> phone: +1.413.773.0611 <tel:%2B1.413.773.0611>
> email: MatthewSirum at gmail.com <mailto:MatthewSirum at gmail.com>
>
>
> -------- Original Message Below --------
>
> [RE-wrenches] Third Radian
>
> William Miller william at millersolar.com <http://millersolar.com/>
> Tue Apr 25 23:03:03 PDT 2017
>
> Matt:
>
> I have a question for you: I have often considered mounting Class T fuses
> directly to a bus bar as you have done. Are you ever worried about physical
> strain on the fuse itself without a fuse holder?
>
> Thanks again for all of your input.
>
> William Miller
>
> Lic 773985
> millersolar.com <http://millersolar.com/>
> 805-438-5600 <tel:805-438-5600>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> Tump at swnl.net <blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net> www.SWNL.net <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
> Solarwinds Northernlights
> Serving Mid Coast Maine & Northern California
> 207-832-7574 Cl. 610-517-8401
> Blair "TUMP" May
> ******** MAINE'S CHARTER ********
> NABCEP "Certified PV Installer"
>
> ******** MAINE'S CHARTER ********
> Trace Xantrex "Certified" Dealer / Installer"
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170428/47e2b442/attachment.htm>
More information about the RE-Wrenches
mailing list