[RE-wrenches] Aquion tech support

Bradley Bassett bbassett2 at gmail.com
Thu Apr 27 18:39:52 EDT 2017


With the low discharge rate of the Aquion battery, it would have to be a
larger bank to handle 6 Sunny Island inverters. To put out the 36kW to
power those inverters at full rate you'd need at least 40 stacks at a good
state of charge to do that. At lower state of charge or if they are the
older versions like S20 or S30 you'd probably need more stacks to handle
it. I have a note indicating that SMA considered 16 stacks to be the
minimum for each Sunny Island. That would be 96 stacks.

Brad

On Wed, Apr 26, 2017 at 9:38 AM, Tump <tump at swnl.net> wrote:

> Hate to be an ass, but look in the mirror! There is NONE! The battery set
> point voltage w/ the SMA Aquion BM200 is ~57.5V UNLIKE all the other
> inverter manu’s suggestions of 59.8 V. Contact me off list if you want
> additional thoughts. TUMP
>
> On Apr 26, 2017, at 12:31 PM, garyh at solarindependence.com wrote:
>
> I am scheduled to be going out to a site in a couple of weeks that is
> experiencing frequent shutdowns and I've offered to investigate why the
> shutdowns are occurring. The site is 208 3 phase with six Sunny Islands and
> Aquion batteries. I've got SMA tech support aware in case I need to talk
> with them but not Aquion. Does anyone have a technical contact for Aquion
> at this time??
> Gary
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> *Tump at swnl.net*               *www.SWNL.net*
>                 Solarwinds Northernlights
> *       Serving Mid Coast Maine & Northern California*
> *                         207-832-7574 <(207)%20832-7574>   Cl.
> 610-517-8401 <(610)%20517-8401>                              *
>                               *Blair "TUMP" May*
>
>
> *               ********  MAINE'S CHARTER ******** *                   *
> NABCEP    "Certified PV Installer"*
>
>
> *                 ********  MAINE'S CHARTER ********          **
> Trace Xantrex "Certified" Dealer / Installer"*
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170427/86b03d81/attachment.htm>


More information about the RE-Wrenches mailing list