[RE-wrenches] NEC 705.12(B)(2)(3)(c) intention
Mark Frye
markf at berkeleysolar.com
Wed Apr 19 19:18:25 EDT 2017
If your sketch shows that there are 200A of breakers in the sub panel
and 200A of breakers in the main, then, no, that would not be the
intent. The lug kit makes the two separate bars into a single bar.
Mark
On 4/19/2017 3:29 PM, August Goers wrote:
>
> Hi Wrenches –
>
> Now that we’re in the 2014 NEC, we’ve increasingly been using the NEC
> 705.12(B)(2)(3)(c) interconnection method:
>
> imap://markf@mail.lmi.net:143/fetch%3EUID%3E.Re-Wrenches%3E12200?header=quotebody&part=1.1.2&filename=image001.png
>
> This is a great way of putting lots of PV on a panel when there are
> few loads. As long as the total breaker rating (excluding the supply
> breaker) equals the bus rating or less, we’re good to go. However, we
> recently ran into a panel that had a lug subfeed kit installed in it.
>
> Do you think the intention of the code is to allow something like
> shown in this sketch?
>
> Cheers,
>
> August
>
> Luminalt
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170419/d460cc7e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 41287 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170419/d460cc7e/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 228574 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170419/d460cc7e/attachment-0001.png>
More information about the RE-Wrenches
mailing list