[RE-wrenches] Polaris gone bad?

Off Grid Solar offgridsolar at sti.net
Sun Apr 9 11:12:06 EDT 2017


It is always ideal to not have to splice except when the reality of coming
in on a job that is old work, someone who did not follow basic code
requirements, an insurance situation, an existing equipment upgrade, an
insurance situation, a remote home, a really remote home you had to fly
to, a 2000 foot run to an array and you hit granite, or Telcom. I could
remember a few more with some time.

I almost always use a Square D 3phase HV disco at the array and that is my
combiner/JB/transition. I can safely connect 2 strings and many KW of
solar all in one box. Add the fuses and 3 strings in one box. That is
ideal for me!
Sometimes ideal is the goal that is not always achieved:)





> William,
>    The only place we use splicing is in the transition box, where we
> transition from USE/RHW or PV wire to THWN in conduit. We almost always
> have this transition in smaller systems without need of a combiner box.
> I suspect it is the same for others. In larger systems there is no need
> for splicing anywhere with the use of combiner boxes.
>
> Daryl
>
>
>
>> Wrenches:
>>
>> I am wondering why the proliferation of splices in PV leads?  We all
>> know
>> splices are a weak link.
>>
>> We allow only one connection between a module and the feeder
>> destination--
>> be it a combiner, inverter or optimizer-- and it is an MC connector, one
>> side of which is factory-made and provided by the module manufacturer.
>>
>> If one plans and pulls PV circuits with forethought, splices should not
>> be
>> necessary.
>>
>> If anyone wants to know more about how this can be accomplished, look at
>> our web site or contact me off list.
>>
>> William
>>
>>> On Apr 8, 2017, at 10:05 AM, Glenn Burt <glenn.burt at glbcc.com> wrote:
>>>
>>> It is also worth noting that many of the SMA installation manuals
>>> specifically say do not use wire nuts on DC wiring.
>>> Of course choosing to ignore the manufacturers installation
>>> instructions
>>> would be a NEC violation.
>>> From: Drake
>>> Sent: ‎4/‎8/‎2017 12:10
>>> To: RE-wrenches
>>> Subject: Re: [RE-wrenches] Polaris gone bad?
>>>
>>>
>>> At 01:35 PM 4/6/2017, you wrote:
>>>> Recently we interfaced with another solar install firm that has gone
>>>> back to wire nuts due to this same problem.
>>>
>>> Wire nuts have the advantage of holding the wires tight with a spring.
>>> The spring follows the cold flow of the copper over the years. A screw
>>> type connection does not.
>>>
>>> When I service an old breaker box, usually the wires are loose under
>>> the
>>> screw connections, especially on the neutral and grounding bars. Often
>>> they are very loose, and I bet that the screws were tight after the
>>> initial installation of the equipment.
>>>
>>> On old industrial control equipment, I've learned the hard way to
>>> tighten all screws before doing anything in the box, as wires are prone
>>> to fall out of the loose screw connections. Again, these connections
>>> have the weakness of being held by terminal screws, with no spring to
>>> follow the cold flow of the metal.
>>>
>>> With wire nuts, it can be a bit tricky to know if you have a good
>>> connection, as the connection is hidden under the plastic cap. It is
>>> good to pull hard on each wire separately to be sure it is securely
>>> under the spring. It is crucial never to mix copper and aluminum under
>>> a
>>> wire nut unless it is one specifically designed for the purpose. Unless
>>> specifically listed, all out door wire nuts should be in a weather
>>> proof
>>> box, and preferably taped.
>>>
>>> Drake Chamberlin
>>> Athens Electric LLC
>>> OH License 44810
>>> CO License 3773
>>> NABCEP Certified Solar PV
>>> 740-448-7328
>>> http://athens-electric.com/
>>>
>>> 	Virus-free. www.avast.com
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>




More information about the RE-Wrenches mailing list