[RE-wrenches] Sunny Island no Longer Supports TLs - How about New Series?

Ray ray at solarray.com
Sun Mar 26 15:00:09 EDT 2017


First, its the added cost of the disconnecting combiner, RT breakers, 
control boards, Main initiator, and extra labor for wiring and testing.  
I'd say it ads another $2 to $3K of cost. Not a big deal on large 
systems but for a smaller off grid project in the $10K range, its a huge 
increase in cost.  Folks are just going to go DIY with junk off the 
internet, and the code is now under the bus.

We've successfully argued that 690.12 only applies to the PV array 
circuit, not the inverter and battery output.  Which has at least kept 
refrigerators and heating system on during a trip. However, because 
charge controllers hold residual voltage in capacitors after the array 
is disconnected, we have had to add RT breakers at the charge 
controllers to comply with the 30 v in 10 sec rule.

My main issue is safety: if the system trips, the customer must go onto 
the roof to manually reset the combiner box to restore power. IMO, we 
have inadvertently traded customer safety in the name of fire fighter 
safety, not a fair bargain at all.  There are numerous nuisance faults 
that require reset, (CAT 5 loose connection or induced noise, faulty 9 v 
battery, naughty neighbor) Firefighters will probably only ever be on 
site to strap our poor customer to a back board after they fall off the 
roof in the snow trying to reset their new 690.12 compliant system.

R. Ray Walters
Chief Technical Officer, RemoteSolar.com
BS Mech Engineering, 1988
Former NABCEP Certified, 2004-2016
Licensed Master ELectrician, Colorado
303 505-8760

On 3/26/17 9:22 AM, Dan Fink wrote:
> Hello Ray -- Can you elaborate on why these battery-based projects are 
> getting killed here locally? Is it the misinterpretation by AHJs that 
> 690.12 has to disconnect the inverter from the battery bank with giant 
> shunt-trip breakers? If that were the case...backup generators would 
> have to be controlled by rapid shutdown too, and I don't think that 
> can of worms has been opened yet.
>
> Dan Fink
> Professor of Solar Energy Technology, Ecotech Institute
> IREC Certified Instructorâ„¢ for:
> ~ PV Installation Professional
> ~ Small Wind Installer
> Executive Director, Buckville Energy
> NABCEP Registered Continuing Education Providersâ„¢
> 970.672.4342 <tel:970.672.4342>
>
>
> On Sat, Mar 25, 2017 at 8:04 PM, Ray <ray at solarray.com 
> <mailto:ray at solarray.com>> wrote:
>
>     Not to muddy the waters, but how does the SMA system deal with
>     690.12 Rapid Shutdown requirements in OG and GTB arrangements? 
>     690.12 has been killing battery based projects left and right here
>     in Colorado.
>
>     Thanks,
>
>     R. Ray Walters
>     Chief Technical Officer, RemoteSolar.com
>     BS Mech Engineering, 1988
>     Former NABCEP Certified, 2004-2016
>     Licensed Master ELectrician, Colorado
>     303 505-8760 <tel:%28303%29%20505-8760>
>
>     On 3/25/17 6:46 PM, Jeff Clearwater wrote:
>>     Hi Howie,
>>
>>     So Jay found this from previous posts (below).  So apparently the
>>     -40 series will work in Off-grid mode (as long as you program the
>>     SBs separately to be in OG) but won't do the switching of modes
>>     necessary for grid-tie backup.  I plan on a call to SMA tech
>>     support Monday morning to get to the bottom of what exactly is
>>     lost without the RS485 comm.  And to see if TLs are still going
>>     to work as the new SIs tech sheet shows they are not supported. 
>>     why I have no idea but I intend to find out.
>>
>>     hope that helps.
>>
>>     Best,
>>
>>     Jeff
>>
>>>     Begin forwarded message:
>>>
>>>     *From: *Drake <drake.chamberlin at redwoodalliance.org
>>>     <mailto:drake.chamberlin at redwoodalliance.org>>
>>>     *Subject: **Re: [RE-wrenches] SMA US 40 & AC coupling*
>>>     *Date: *March 13, 2017 at 10:23:56 AM PDT
>>>     *To: *RE-wrenches <re-wrenches at lists.re-wrenches.org
>>>     <mailto:re-wrenches at lists.re-wrenches.org>>
>>>     *Reply-To: *RE-wrenches <re-wrenches at lists.re-wrenches.org
>>>     <mailto:re-wrenches at lists.re-wrenches.org>>
>>>
>>>     I talked with Tim at SMA today, and the new Sunny Boy inverters
>>>     will  provide taper charging with the Sunny Islands even though
>>>     no RS 485 communication is available. The Sunny Boys need to be
>>>     programmed in the off grid mode, and the Sunny Islands will take
>>>     care of the UL 1741 requirements.
>>>
>>>     The graph below shows the relation between frequency shift and %
>>>     power produced by the Sunny Boy inverters.
>>>     Emacs!
>>>
>>>     Drake Chamberlin
>>>     /Athens Electric LLC
>>>     OH License 44810
>>>     CO License 3773
>>>     NABCEP Certified Solar PV
>>>     740-448-7328 <tel:%28740%29%20448-7328>
>>>     /http://athens-electric.com/
>>>     At 11:36 AM 3/10/2017, you wrote:
>>>     I just checked with SMA and they do not have an RS485 card for
>>>     the -40 inverters. What this means is that you can set them up
>>>     to be permanently in off grid mode where the SB will follow the
>>>     frequency shift of the SI, ok for an off grid system. But for
>>>     grid tie with backup, the SB will not communicate with the SI
>>>     and will not change the SB to off grid mode. It will still work
>>>     like other generic AC coupled systems where the frequency shift
>>>     will cause the SB inverter to drop off line, but as far as I
>>>     know no throttling back will happen.
>>>
>>>     Brad
>>
>>
>>     Howie Michaelson wrote:
>>>     I'm confused. Does this mean the -40 series are not compatible
>>>     with SI off grid mode? Or they don't adjust output due to
>>>     frequency shift? Or?
>>>
>>>     Howie
>>>     Howie Michaelson
>>>     NABCEP Certified Solar PV Installerâ„¢
>>>
>>>     Sun Catcher
>>>     Renewable Energy Systems Sales and Service
>>>     VT Solar Electric Incentive Partner
>>>     802-272-0004 <tel:%28802%29%20272-0004>
>>>
>>>     On Mar 25, 2017 7:59 PM, "Tump" <tump at swnl.net
>>>     <mailto:tump at swnl.net>> wrote:
>>>
>>>         Jeff the bad news is yer outa luck BUT they "had a work
>>>         around" that was discussed on the list a few weeks ago. I
>>>         looked quickly but didn’t see it posted. You were going to
>>>         install a RS 485 card/ module that had the soft ware to make
>>>         it work. I found this out just as these “Newest latest n
>>>         greatest inverters" were just coming out, looked at the
>>>         manual, and much to my disappointment I had to send it back
>>>         and educate my salesperson to this. Lucky for me I was able
>>>         to get the TL series. Ill keep on looking, if you don’t have
>>>         any luck I do have a contact at SMA…. at least he was there
>>>         2 weeks ago, contact me off list. Tump
>>>>         On Mar 25, 2017, at 12:10 PM, Jeff Clearwater
>>>>         <jeffc at villagepowerdesign.com
>>>>         <mailto:jeffc at villagepowerdesign.com>> wrote:
>>>>
>>>>         All,
>>>>
>>>>         Can anyone confirm for me that the SUNNY BOY 3.0-US /
>>>>         3.8-US / 5.0-US / 6.0-US / 7.0-US / 7.7-US series is or is
>>>>         not supported by the Sunny Island in off-grid AC coupling
>>>>         mode?  The technical paper on the subject here
>>>>         http://files.sma.de/dl/7910/SB-OffGrid-TI-US-en-18.pdf
>>>>         <http://files.sma.de/dl/7910/SB-OffGrid-TI-US-en-18.pdf>
>>>>         does not list them but I'm hoping it's cause that paper is
>>>>         dated Feb '16.
>>>>
>>>>         I sure hope they are because that paper shows they
>>>>         discontinued support the the  SUNNY BOY 3000TL-US /
>>>>         3800TL-US / 4000TL-US / 5000TL-US / 6000TL-US / 7000TL-US /
>>>>         7700TL-US series!  Why!??
>>>>
>>>>         Hope you have good news for me!
>>>>
>>>>         Best,
>>>>
>>>>         Jeff
>>>>
>>>>         -- 
>>>>         Jeff Clearwater
>>>>         Village Power Design
>>>>         Renewable Energy Design & Installation
>>>>         Ecovillage Design Consultant
>>>>
>>>>         Licensed Solar Contractor in CA - C-46
>>>>         www.villagepowerdesign.com <http://www.villagepower.com/>
>>>>         413-559-9763 <tel:%28413%29%20559-9763>
>>>>         ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
>>>>
>>>>         _______________________________________________
>>>>         List sponsored by Redwood Alliance
>>>>
>>>>         List Address: RE-wrenches at lists.re-wrenches.org
>>>>         <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>
>>>>         Change listserver email address & settings:
>>>>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>         <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>
>>>>         List-Archive:
>>>>         http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>         <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>>>>
>>>>         List rules & etiquette:
>>>>         www.re-wrenches.org/etiquette.htm
>>>>         <http://www.re-wrenches.org/etiquette.htm>
>>>>
>>>>         Check out or update participant bios:
>>>>         www.members.re-wrenches.org
>>>>         <http://www.members.re-wrenches.org>
>>>>
>>>
>>>>         *Tump at swnl.net**www.SWNL.net*
>>>>         Solarwinds Northernlights *//*
>>>>         */     Serving Mid Coast Maine & Northern California/**/
>>>>         /**/207-832-7574 <tel:%28207%29%20832-7574>   Cl.
>>>>         610-517-8401 <tel:%28610%29%20517-8401> /*
>>>>         *//**/Blair "TUMP" May/*
>>>>
>>>>         */ ******** MAINE'S CHARTER ********
>>>>         /**//**/  NABCEP    "Certified PV Installer"/**/
>>>>         /**/
>>>>         ******** MAINE'S CHARTER ********
>>>>         /**/        Trace Xantrex "Certified" Dealer / Installer"/*
>>>>
>>>>
>>>
>>>
>>>
>>>         _______________________________________________
>>>         List sponsored by Redwood Alliance
>>>
>>>         List Address: RE-wrenches at lists.re-wrenches.org
>>>         <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>         Change listserver email address & settings:
>>>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>         <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>
>>>         List-Archive:
>>>         http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>         <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>>>
>>>         List rules & etiquette:
>>>         www.re-wrenches.org/etiquette.htm
>>>         <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>         Check out or update participant bios:
>>>         www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>
>>>
>>>     _______________________________________________
>>>     List sponsored by Redwood Alliance
>>>
>>>     List Address:RE-wrenches at lists.re-wrenches.org
>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>     Change listserver email address & settings:
>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>     <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>
>>>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>     <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>>>
>>>     List rules & etiquette:
>>>     www.re-wrenches.org/etiquette.htm
>>>     <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>     Check out or update participant bios:
>>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>
>>     -- Jeff Clearwater Village Power Design Renewable Energy Design &
>>     Installation Ecovillage Design Consultant NABCEPâ„¢ Certified Solar
>>     PV Installer Licensed Solar Contractor in CA - C-46
>>     www.villagepowerdesign.com <http://www.villagepower.com>
>>     413-559-9763 <tel:%28413%29%20559-9763>
>>     ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
>>
>>     _______________________________________________
>>     List sponsored by Redwood Alliance
>>
>>     List Address:RE-wrenches at lists.re-wrenches.org
>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>>     Change listserver email address & settings:
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>     <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>
>>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>     <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>>
>>     List rules & etiquette:
>>     www.re-wrenches.org/etiquette.htm
>>     <http://www.re-wrenches.org/etiquette.htm>
>>
>>     Check out or update participant bios:
>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>     _______________________________________________ List sponsored by
>     Redwood Alliance List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org> Change listserver email
>     address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>     <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>     <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>     List rules & etiquette: www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm> Check out or update
>     participant bios: www.members.re-wrenches.org
>     <http://www.members.re-wrenches.org> 
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170326/85336c3e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27098 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170326/85336c3e/attachment.jpe>


More information about the RE-Wrenches mailing list