HI Glenn,
I have not X%#&*? idea of what the building department is thinking.
They would take a sign off from a, and I quote here “california licensed professional” And that is what exactly?
But yes you are correct.
200 amp 208v 3 phase service
2 existing 3kw SMA inverters
this was adding the 3rd.
Utility was fine with the other two which were added one at a time. ( 1 per year, this being year 3)
Jay
Peltz power
> On Mar 24, 2017, at 5:09 PM, Glenn Burt <glenn.burt at glbcc.com> wrote:
>
> HI Jay,
>
> Are they saying that adding the 3rd inverter will cause a greater than 3% imbalance?
> How big are the inverters? Are they all the same size?
> Is it a 208 or 480 service?
>
> -Glenn
>
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jay
> Sent: Wednesday, March 22, 2017 8:47 PM
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] 2014 NEC 705-100 (A)
>
> Hi Glenn
>
> I had it correct in the subject, but got it wrong below, here is the correct number
>
>
>
> 2014NEC, 705-100 (a)
>
>
>
> On Mar 21, 2017, at 8:09 PM, Glenn Burt <glenn.burt at glbcc.com <mailto:glenn.burt at glbcc.com>> wrote:
>
>> Hi Jay,
>> I must not understand.
>> I don't see a 705.11 in the 2014 NEC.
>> From: jay <mailto:jay.peltz at gmail.com>
>> Sent: 3/21/2017 21:34
>> To: RE-wrenches <mailto:re-wrenches at lists.re-wrenches.org>
>> Subject: [RE-wrenches] 2014 NEC 705-100 (A)
>>
>> HI All,
>>
>> I’ve got a client who’s having some issues with the building department. (for the 705-11-A NEC 2014)
>> Now it is true that we in California are now in 2014 NEC)
>> They are saying that he isn’t allowed to install the 3rd inverter onto a 3 phase service
>> ( this system was done in stages, using SMA 3kw for phases 1 and 2)
>> Now they are being stopped on adding the 3rd.
>>
>> Anyone ever run into this before?
>> Any answers?
>>
>> thanks
>>
>> jay
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/><wp_ss_20170321_0001.jpg>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>_______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20170325/2625eadc/attachment.htm>
More information about the RE-Wrenches
mailing list