[RE-wrenches] Conext SW 4024 with bad firmware
William Miller
william at millersolar.com
Thu Dec 29 15:59:27 EST 2016
Lou:
I am sorry to hear about your situation. Too often the installer is stuck
in the middle between equipment that does not perform as it should and the
customers that experience the problems.
I have a system with similar problems, although it is an Outback system.
The facility is an off-grid state highway maintenance station. The loads
are large, the PV small and therefore requires two generator run time per
day. The load profile shows peak loads in mornings and evenings. We
figured the best way to accommodate this profile was to have two must-run
periods per day. The Outback equipment does not support two must-run
cycles per day.
The generator runs were achieved by using an external time clock set for
two closures per day. The problem is the generator shuts down without the
system knowing. If the system knew about the shutdown, it would disconnect
first and stop generator second. If your inverter is starting and stopping
the generator, it should disconnect first. If it is not doing so, the
logic is faulty. This may be what the firmware fails to do. If so, this
is a very basic flaw in the firmware. This concept is quite old and should
have been incorporated in the system without second thought.
In our case, the generator shutdown generates a lot of error codes due to
decaying voltage and frequency. We minimized the errors by shortening the
transfer delay. If this parameter exists in the Conext system, it may be
called something different from the term Outback uses, so you will have to
determine for yourself if this adjustment exists. If you find it, set it
to transfer at a high threshold (nearer 120/240 at 60 hertz) and as quickly
as possible.
This may not be possible, but see if you can adjust your way out of this
problem.
Good luck.
William Miller
[image: Gradient Cap_mini]
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Lou Russo
*Sent:* Thursday, December 29, 2016 11:27 AM
*To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
*Subject:* [RE-wrenches] Conext SW 4024 with bad firmware
Wrenches,
I recently installed a Schneider Conext SW 4024, Schnieder's DC
Distribution panel, AC Distribution panel, SCP, and the AGS. It was to be a
straightforward inverter swap, Xantrex 4024 to the Conext SW setup. The
actual installation went fine. I did switch over the house wiring from 120
to 240 as well as the diesel genset.
After a steep learning curve with the client all seemed well. 1 week later
she called and says the power behaves oddly as the generator is shutting
down. Symptoms are some arc fault breakers trip and the compressor on her
fridge sounds like its bogging down. I make the 45 minute drive out and
started my search. This is a site with 3 buildings on 3 acres. I double
checked all my wiring at the inverter, then moved onto the various
buildings checking for redundant neutral to grounds, proper bonding, etc…
Surprisingly although not great workmanship everything is where it is
supposed to be. I decided to give the AC input on the inverter it's own
dedicated neutral as at this point I was reaching for straws and the
installation manual was unclear about this detail. Still nothing. A call to
Schnieder confirmed that there was no setting I was missing.
I placed another call to Schnieder tech support. They did and have
continued to answer the phone promptly. It did take a bit of chasing them
but I finally got a answer that there Level 3 folks can reproduce the
error. The inverter is following the frequency of the genset as it winds
down down to 40hrtz. This is after the AC transfer inside the inverter has
happened. During the cool down period everything is fine. This happens as
the genset is actual shutting off and spinning down to a stop. They say
this a firmware issue and that it will take months to push out as is needs
to be UL listed. In the meantime I have a pissed off client, her oven went
belly up on the low frequency voltage, there is concern about possible
unseen damage to her new water pump, and I wasted countless hours of my
own time attempting to make the situation right. All of this due to a
firmware that was released with a fatal flaw and can not be changed for
months.
I am extremely disappointed in Schneider. I have been hesitant use them
over the years as I was still scarred from the Xantrex days. My “beta” test
went will with a early version I installed 2 years ago so I figured it was
a safe move. Obviously I was wrong. Lesson learned stick with Outback and
SMA.
So I have 2 questions for the list.
1.Has anybody else on the list seen this issue and corrected it regardless
of the firmware? I have installed one other conext sw about 2 years ago
when it first came out. The setup is very similar except that it is 48V and
has a very old firmware. I went out to this old site to confirm all is well
and it is fine.
2.Does anybody have a good contact at Schneider that could be of help? I
tried to contact Sandra Herrera as she was a great help years ago, but her
phone number no longer works.
3.Does anybody have an old version of the Conext firmware lying around they
could point me to? The website does not seem to have old versions.
Any input is greatly appreciated!
Schnieder, if you have a presence here contact me.
Aloha,
Lou Russo
lou at spreesolarsystems.com
440 345 6762
Spree Solar Systems LLC
CT-34322
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20161229/8f7b06f3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20161229/8f7b06f3/attachment.jpg>
More information about the RE-Wrenches
mailing list