[RE-wrenches] Conext SW 4024 with bad firmware

Jay jay.peltz at gmail.com
Thu Dec 29 15:03:11 EST 2016


Hi Lou,

I might suggest a relay that switches with the signal for ags start/stop. 
It'll disconnect the AC from the genset with a lot shorter delay. 

Jay

Peltz power. 



Sent from my iPhone

> On Dec 29, 2016, at 11:27 AM, Lou Russo <lou at spreesolarsystems.com> wrote:
> 
> Wrenches,
> 
> I recently installed a Schneider Conext SW 4024, Schnieder's DC Distribution panel, AC Distribution panel, SCP, and the AGS. It was to be a straightforward inverter swap, Xantrex 4024 to the Conext SW setup. The actual installation went fine. I did switch over the house wiring from 120 to 240  as well as the diesel genset. 
> 
> After a steep learning curve with the client all seemed well. 1 week later she called and says the power behaves oddly as the generator is shutting down. Symptoms are some arc fault breakers trip and the compressor on her fridge sounds like its bogging down. I make the 45 minute drive out and started my search. This is a site with 3 buildings on 3 acres. I double checked all my wiring at the inverter, then moved onto the various buildings checking for redundant neutral to grounds, proper bonding, etc… Surprisingly although not great workmanship everything is where it is supposed to be. I decided to give the AC input on the inverter it's own dedicated neutral as at this point I was reaching for straws and the installation manual was unclear about this detail. Still nothing. A call to Schnieder confirmed that there was no setting I was missing. 
> 
> I placed another call to Schnieder tech support. They did and have continued to answer the phone promptly. It did take a bit of chasing them but I finally got a answer that there Level 3 folks can reproduce the error. The inverter is following the frequency of the genset as it winds down down to 40hrtz. This is after the AC transfer inside the inverter has happened. During the cool down period everything is fine. This happens as the genset is actual shutting off and spinning down to a stop. They say this a firmware issue and that it will take months to push out as is needs to be UL listed. In the meantime I have a pissed off client, her oven went belly up on the low frequency voltage, there is concern about possible unseen damage to her new water pump, and I  wasted countless hours of my own time attempting to make the situation right. All of this due to a firmware that was released with a fatal flaw and can not be changed for months. 
> 
> I am extremely disappointed in Schneider. I have been hesitant use them over the years as I was still scarred from the Xantrex days. My “beta” test went will with a early version I installed 2 years ago so I figured it was a safe move. Obviously I was wrong. Lesson learned stick with Outback and SMA. 
> 
> So I have 2 questions for the list.
> 
> 1.Has anybody else on the list seen this issue and corrected it regardless of the firmware? I have installed one other conext sw about 2 years ago when it first came out. The setup is very similar except that it is 48V and has a very old firmware. I went out to this old site to confirm all is well and it is fine.
> 
> 2.Does anybody have a good contact at Schneider that could be of help? I tried to contact Sandra Herrera as she was a great help years ago, but her phone number no longer works. 
> 
> 3.Does anybody have an old version of the Conext firmware lying around they could point me to? The website does not seem to have old versions.   
> 
> Any input is greatly appreciated!
> 
> Schnieder, if you have a presence here contact me. 
> 
> 
> Aloha,
> 
> Lou Russo
> lou at spreesolarsystems.com
> 440 345 6762
> Spree Solar Systems LLC 
> CT-34322
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20161229/ec40a2bb/attachment.htm>


More information about the RE-Wrenches mailing list