August,

Great question.

Canadian Solar makes a module with SolarEdge optimizers integral.  Trina
offers a similar product with Tigos integral.  I think both products would
allow the string architecture you like while incorporating rapid shutdown.
 I have found these solutions to be less expensive than microinverters for
systems over 4 kW though not necessarily less expensive than standard
modules, strings inverters, and rapid disconnect enclosures.  We have been
trying to specify these module-integral products.

Curious to hear how others are proceeding.

Matt



On Wed, December 14, 2016 10:20 am, August Goers wrote:
> Hi Wrenches,
>
>
>
>
> We are adopting the 2014 NEC in just a few weeks and will be installing
> NEC
> 690.12 rapid shutdown compliant systems for all permits pulled on or after
>  Jan 1 2017. I thought I’d take a quick poll to see what equipment you
> are all planning on using to comply with rapid shutdown for your
> residential systems. Some of you are operating in states where you’ve been
> rapid shutdown for the last couple of years so you might have valuable
> insight as well.
>
>
>
> We have historically had the best reliability results with string
> inverters and have tried to continue to use them. However, multiple forces
> are drawing us towards microinverter systems (or AC modules) and optimized
>  systems like SolarEdge. For one, our sales reps and designers prefer the
>  design freedom that these types of systems offer. The module level
> monitoring is also a big plus. Secondly, we are installing a lot of
> SunPower Equinox AC module systems and the install times are smokin’
> fast. Lastly, these systems are rapid shutdown compliant with little or no
>  additional effort.
>
>
>
> I really like SMA inverters but their rapid shutdown solution seems
> clunky, especially when paired with their new US-40 series inverters which
> have three trackers. The rapid shutdown box only has two separate tracker
> capability so we would need to install two rapid shutdown boxes to make
> use of the three trackers. Other string inverter options like Fronius
> might be a little easier to design around.
>
>
>
> So, for now we are offering SunPower’s Equinox AC system and SolarEdge
> for an alternative. I like many aspects of Enphase’s microinverter system
> but still feel gun-shy because of all the failures we’ve had. Maybe their
> newer generation products have solved their reliability problems.
>
>
>
> What are you all using?
>
>
>
>
> Best,
>
>
>
>
> August
>
>
> Luminalt
>
>
> San Francisco
> _______________________________________________
> List sponsored by Redwood Alliance
>
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.ht
> ml
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


Matthew Partymiller
Solar Energy Solutions LLC
(877) 312-7456
matt at solar-energy-solutions.com




More information about the RE-Wrenches mailing list