[RE-wrenches] Fwd: RE: Grid neutral
Drake
drake.chamberlin at redwoodalliance.org
Sat Nov 26 11:25:20 EST 2016
A 120/240 V split phase system is supplied by a
center tapped 240 V transformer. The center tap
is grounded, deriving the neutral. Unbalanced
current from the two hot phase conductors return back through the neutral.
At 08:27 PM 11/25/2016, you wrote:
>Wrenches,
>Is there such a thing as a "grid neutral"? I
>have been providing design support to a client
>for a large off grid system; a prepper, rare in
>these parts. He claims that utility current is
>carried in part through the ground and in part
>through a neutral conductor, and such a "utility
>neutral" is deliberately undersized. At first I
>pushed back (see below). Now I just wonder what
>Wrenches more knowledgeable than I am will say.
>Thank you,
>Allan
>
>Allan Sindelar
><mailto:allan at sindelarsolar.com>allan at sindelarsolar.com
>NABCEP Certified PV Installation Professional
>NABCEP Certified Technical Sales Professional
>New Mexico EE98J Journeyman Electrician
>Founder (Retired), Positive Energy, Inc.
>505 780-2738 cell
>
>-------- Forwarded Message --------
>Date: Thu, 24 Nov 2016 11:25:36 -0700
>
>Allan
>Happy thanksgiving. Sorry for the slow reply; overwhelmed here.
>
>All wet sorry. If you look at the power lines
>you will see two or three wires at top of pole
>and the one smaller one a little ways down the
>pole. This is the power station neutral.
>
>The hots bidirectional is an explanation that
>helps people understand current but is not totally clear.
>Even if you use that visualization in order for
>the electrons on the hot to oscillate they heed
>a path to oscillate into and out of
>That is the neutral.
>
>Bottom line is from the power station and in
>your home you have at least one hot and one neutral.
>You can actually use the hot to light up a lite
>bulb by connecting the other side of the lite bulb to the earth.
>This one way you can get electrocuted.
>I touched the hot side of a 220 circuit and the
>current went thru me and into the earth
not much fun.
>
>This has been openly publicly discussed and one
>of the electrical association advised the power
>companies to increase the size of the neutral to
>solve many issues, such as cows giving less milk
>and problems with electric current in homes. The
>power companies even openly discuss this.
>
>In remote rural areas of Australia, I have seen
>electricity distribution using SWER (Single-Wire
>Earth Return); just one wire is fed to the
>property at a high voltage, with the current
>returning via the ground. At the property, a
>transformer turns the high voltage into normal
>residential voltages on a pair of wires (230VAC
>in Australia vs 2x115V in some other countries).
>But this SWER system is inefficient, and the
>supply voltage is poorly regulated; it is a rare
>exception - it is only done because of the high
>cost of delivering two wires in remote areas.
>
>In metropolitan areas, you will typically see 4
>wires passing down the street. This consists of
>three phases of "Active", plus a "Neutral". You
>could imagine the Active carrying current "from"
>the power grid, and the Neutral carrying the
>current "back to" the power grid (even though the current flow is symmetrical).
>
>There is lots of info online if you wish to learn more about this.
>Take care, Robert
>
>From: Allan Sindelar
>[<mailto:allan at sindelarsolar.com>mailto:allan at sindelarsolar.com]
>Sent: Sunday, October 23, 2016 10:18 PM
>
>Robert,
>I'm neither an electrical engineer or a utility
>employee, so I may be all wet here, and if so
>please dry me off with a straight-up
>explanation. But this whole argument seems
>specious to me, as it addresses a "grid neutral".
>
>My reasoning is this - there is no such animal
>as a "grid neutral" in utility lines, so how is
>this issue even relevant? The "hots" are
>bidirectional; only when the utility power is
>stepped down at the transformer at the home is a
>reference neutral created. To say that the
>current "cannot all go back thru the neutral
>since it is not large enough BY DESIGN" seems to
>me an absurd concept since there is no neutral in utility power distribution.
>
>Am I missing something?
>Allan
>
>On 10/2/2016 7:51 PM, Robert wrote:
>Allan
>Here is the info I said I would send:
><https://www.youtube.com/watch?v=aJOB2FIqUiQ>https://www.youtube.com/watch?v=aJOB2FIqUiQ.
>Listen about 20 minutes at least.
>
>All current that goes out on the two
>residential or three commercial hots goes back on the grid neutral
>AND thru the ground'. It cannot all go back thru
>the neutral since it is not large enough BY
>DESIGN. So
. That means we really dont have a clean ground anymore.
>
>Thank you for your time today. It is enjoyable to speak with you.
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20161126/fa3fb50d/attachment.htm>
More information about the RE-Wrenches
mailing list