[RE-wrenches] SMA Arc-Fault
Drake
drake.chamberlin at redwoodalliance.org
Fri Nov 11 10:15:11 EST 2016
Electrical noise coming in from the utility side
can also cause an arc fault code.
At 07:32 AM 11/11/2016, you wrote:
>This array is a ground mount, so not on a roof, and no radio towers nearby.
>
>As for grounding, The array and the shed with
>the interconnection point are in the same area.
>There are a couple ground rods there, which
>everything on the AC side is connected to,Â
>including a #6 wire from each inverter. there is
>just a #10 ground coming from the array to the inverters.Â
>The house is a couple hundred feet away and has
>its own grounding electrode system.
>
>Jerry,
>The inverters are new (replaced 2 months ago),
>but it is a good idea to check firmware.
>As for AC loads, nothing stands out as the types
>of things you mentioned, although there
>may be a well pump. They also do have a large
>water storage tank for heating, but they
>say that they have not needed to use it yet this
>year. Then there is also the generator...
>
>Thanks for your recommendations.
>-Dave
>
>
>
>--
>
>Dave Tedeyan
>Project Engineer
>
>Taitem Engineering, PC
>109Â S. Albany Street, Ithaca, NY 14850
>Voice:Â (607) 277-1118 x121
><http://www.taitem.com/>www.taitem.com
>
>On Thu, Nov 10, 2016 at 9:51 PM, Jerry Shafer
><<mailto:jerrysgarage01 at gmail.com>jerrysgarage01 at gmail.com> wrote:
>Dave.
>We have many TL-22 in the field and they will
>detect faults even when they are normal
>contactor faults, have you made sure the SW is
>the latest, last I checked it is 2.65.3R and it
>may have a patch in there, you can turn off the
>feature for testing only and see if you melt
>something down but if you do please be on site
>as a arc may happen. Do you have a well, AC
>system with contacts, welders, compressors,
>anything that has a dry contacts that brakes
>under load, this is another place I would look.
>Every time we have had a code out it was real
>weather from something normal or a wire issue.
>Not to brag but we have hundreds in the field
>from the 3's to the 24's and as much as I dread
>getting a call with this issue I can usually
>find the problem and it can be either AC or DC.
>Jerry
>
>On Thu, Nov 10, 2016 at 8:14 AM, Dave Tedeyan
><<mailto:dtedeyan at taitem.com>dtedeyan at taitem.com> wrote:
>Hi All,Â
>
>Maybe someone will have some ideas for why a
>couple inverters keep arc faulting:
>
>-There are two SB7000TL-22 inverters, Sunpower branded.
>-3 Strings of 7 SPR-327's to each inverter. Kept separate until the inverter.
>-Ground mount about 50' from the shed where the
>inverters are located (indoors)
>-Simple grid connected system, no batteries.
>-There is a whole house generator co-located in the shed.
>-We interconnect by using piercing taps on the
>line side of the generator transfer switch
>-There has been only one power outage there
>since the system was installed in April, but the generator fires up weekly.
>
>-The arc faults have been happening on both
>inverters. Sometimes only one at a time,
>sometimes both will go within a day of each other.
>-The events have been approximately one a month,
>but sometimes more, sometimes less.
>
>-We have already checked every single connection
>in the system twice, by two different people.
>-We have replaced the underground wires (and they looked just fine)
>-We have replaced all home runs.
>-We have replaced both inverters.
>-Arc faults are still happening.
>-Arc faults are not always on the same day/time of the week.
>
>I am wondering if this can be caused by the generator?Â
>Has anyone run into a situation like this or something similar?
>
>Thanks for your help,
>Dave
>
>--
>
>Dave Tedeyan
>Project Engineer
>
>Taitem Engineering, PC
>109Â S. Albany Street, Ithaca, NY 14850
>Voice:Â (607) 277-1118 x121
><http://www.taitem.com/>www.taitem.com
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20161111/4fbb584c/attachment.htm>
More information about the RE-Wrenches
mailing list