[RE-wrenches] MATE3 restart
Lones Tuss
ltuss at outbackpower.com
Fri Nov 4 14:08:01 EDT 2016
Hello Mr. Dahl
I believe a Firmware update will be required. Down load the latest Firmware from the OutBack Website onto an otherwise empty SD card. Insert the SD card in the Mate3 then power it up.
If you press and hold the UP button it will force an update.
After the update is complete it might be a good idea to clear the Internal Data Logs.
Press Lock
Enter the password 141
select Settings then System
Scroll down to
Clear Internal Data Log
Then choose yes.
This should get you up and running.
If it does not help email me directly for further assistance.
Take Care sir
Lones Tuss
Applications Engineer
OutBack Power Technologies
17825 59th Ave NE, Suite B, Arlington, WA 98223
360.618.4383 Office | 425.213.8794 Cell
www.outbackpower.com
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Solar
Sent: Friday, November 04, 2016 4:24 AM
To: Wrenches
Subject: [RE-wrenches] MATE3 restart
All,
We have a MATE3 on campus that resets each time you press a button to leave the main screen. For example, we will press the "charger" button followed by pressing the "graph" button, at this point the screen will stall. The other buttons won't work at this point and the MATE will shut off and restart.
Jesse Dahl
NABCEP PV Installation Professional
IBEW Local 292 - Electrician
Electrical/Solar PV Instructor - HCC
Sent from my iPhone
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches