[RE-wrenches] Undercurrent Protection?

eric at harvesthesun.com eric at harvesthesun.com
Tue Nov 1 15:21:37 EDT 2016


Bill et al.,
 
I received a call from Dan and he cleared things up for me. I have a better understanding of what's happening here in this section of the code. Again, thanks for taking the time to spread some knowledge. I really do appreciate you responding to my green inquiry.
 
Still learning, always learning,
 
Eric Stikes
Founding Director & CEO
Good Sun Solar, A CA non-profit corp.
www.goodsun.life
(530)798-3738
 
 
--------- Original Message --------- Subject: Re: [RE-wrenches] Undercurrent Protection?
From: eric at harvesthesun.com
Date: 11/1/16 11:01 am
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>

  Bill,
 
OK. I think I get it. We're protecting against nuisance tripping due to heat build up over time at breaker terminals resulting from continuous loads/sources of current. I understand that you mean an inverter, as a continuous power source, needs to be "allowed" greater flexibility (125%) of current constraint in order to function when you mention having to "withstand" a certain size breaker. However, we're still missing the actual "overcurrent" protection part, no? Obviously there's Article 240. But that's still not setting a max OCPD size, right?...unless I am missing something.
 
I won't blame you if you decide you have more important things to attend than educating me on the nuances of the NEC. I'm still learning and I do greatly appreciate your insight!

 
 
Eric
 
 
--------- Original Message --------- Subject: Re: [RE-wrenches] Undercurrent Protection?
From: billbrooks7 at sbcglobal.net
Date: 10/31/16 5:41 pm
To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>

  Eric,
 
Your reasoning sounds logical, but it is missing the point. Transformers have to be protected by overcurrent devices, similar to wire. Inverters are current limited devices so they only have to be able to withstand a certain size circuit breaker. The current from the inverter is considered continuous so most circuit breakers are designed to operate at 80% of their rating continuously (therefore the requirement to multiply inverter output current by 125%).
  
 Does that make any more sense?
  
 Bill.
  
 Bill Brooks, PE
 Principal
 Brooks Engineering
 3949 Joslin Lane
 Vacaville, CA 95688
 707-332-0761 (office and mobile)
 bill at brooksolar.com (email)
 www.brooksolar.com (web)
  
  
  
 From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of eric at harvesthesun.com
Sent: Monday, October 31, 2016 3:34 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Undercurrent Protection?
 
   I realize this is potentially a stupid question, and one that is long overdue, but here goes:
 
 
 
Why in 690(B) are we setting a minimum threshold on OCPD when we're protecting against over current?
 
 
 
Shouldn't we be setting a maximum threshold...as is done in pretty much all other cases? The way I see it, we should take the array/inverter max output AC current and multiply by 125% to set our min ampacity on wire,
 
and then calc down to find the breaker trade size that lands between the max AC output current and max AC output current times 125%. That way, we avoid nuisance tripping but achieve the max overcurrent protection possible.
 
By following 690(B) we're actually decreasing OCP: Literally, 690(B) is stating that we can have a breaker 100x over the circuit rating, so long as it's not under the circuit rating times 1.25. To me this seems antilogical.
 
 
 
Mr. Brooks?
 
 
 
690.9(B) Overcurrent Device Ratings. Overcurrent device ratings
 
shall be not less than 125 percent of the maximum
 
currents calculated in 690.8(A).
 
 
 
455.7(B)...The overcurrent protection determined
 
from this section shall not exceed 125 percent of the
 
phase converter nameplate single-phase input amperes.
 
 
 
450.4(A)...Such overcurrent device
 
shall be rated or set at not more than 125 percent of
 
the rated full-load input current of the autotransformer.
 

 
 
450.5(A)(2) Overcurrent Protection. An overcurrent sensing device
 
shall be provided that will cause the main switch or commontrip
 
overcurrent protection referred to in 450.5(A)(1) to open if
 
the load on the autotransformer reaches or exceeds 125 percent
 
of its continuous current per-phase or neutral rating.
 
 
 
450.5(B)(2)(b) Ampere Rating. The overcurrent protection shall be
 
rated or set at a current not exceeding 125 percent of the 
 
autotransformer continuous per-phase current rating or
 
42 percent of the continuous-current rating of any seriesconnected
 
devices in the autotransformer neutral connection.
 





 

 

 
Eric Stikes
 
Founding Director & CEO
 
Good Sun Solar, A CA non-profit corp.
 
www.goodsun.life
 
(530) 559-5023
 

_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches at lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
 _______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches at lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20161101/65231e24/attachment.htm>


More information about the RE-Wrenches mailing list