[RE-wrenches] PV Recombiner
Drake
drake.chamberlin at redwoodalliance.org
Wed Oct 12 18:44:10 EDT 2016
Right, the old Trace DC cabinets were bloody
knuckle boxes for sure. Things have come a long
way since those days, and still have a ways to go.
At 02:36 PM 10/12/2016, you wrote:
>Drake:
>Â
>Your point brings to mind the evolution of the BOS cabinet:
>Â
>1.   In the good old days of the SW
>inverter, the DC cabinet was all you got, and it
>was grossly inadequate. Off-the-shelf load
>centers were the only choice for the AC
>side. AC bypassing was a relatively new concept but it could be done.
>2.   Prior to having an approved inverter,
>Outback manufactured a brilliant system of BOS
>that fit the SW, the DR and the future FX series
>of inverters (the PS series). I believe BoB
>Gudgel is responsible for this design and it was genius.Â
>3.   Even with improved BOS, there are the
>shortcomings we have been discussing. There is
>always room for improvement and I am hoping our discussion drives more of that.
>Â
>I too believe that plug-on AC breakers are the
>superior alternative. They are cheap and
>readily available. Generally two load centers
>are required, one for generator fed and one for
>inverter fed. GTBB systems might call for a
>third panel: utility fed. Bypass is the only
>issue that calls for considerations out of the
>ordinary for standard load center
>installations. Most panel manufacturers
>provide limited interlock methods. Where we
>need to interlock more than two breakers we fab
>our own slides. Sure, they are not
>âlistedâ but they are a simple mechanical
>device and I am comfortable using them.
>Â
>There are some challenges to overcome when
>integrating specialized inverter equipment with
>standard electrical components. For example,
>connecting standard load centers to an FX
>inverter is problematic because the FX KOs are
>so far from the mounting surface. This is the
>part of the work that I enjoy immensely. We
>really want to make installations that are
>reliable, efficient to install and look
>good. I have a friend in the entertainment
>industry that once said, âaesthetically
>pleasing installation are more reliable
â True words.
>
>Â
>Thanks for you input.
>Â
>William
>Â
>Â
>Gradient Cap_mini
>
>Lic 773985
><http://www.millersolar.com/>millersolar.com
>805-438-5600
>Â
>From: RE-wrenches
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Drake
>Sent: Wednesday, October 12, 2016 6:36 AM
>To: RE-wrenches
><<mailto:re-wrenches at lists.re-wrenches.org>re-wrenches at lists.re-wrenches.org>
>Subject: Re: [RE-wrenches] PV Recombiner
>Â
>DC breaker systems should be designed similar to
>AC bolt on breaker systems that are used for
>many commercial and industrial applications.
>
>The explanation for the fact that these don't
>exist has to do with the cost of designing and
>listing the equipment. There is no technical
>reason that a DC enclosure needs to be any more
>difficult to wire than an off the shelf AC box.
>
>The AC breakers in any solar enclosure should
>certainly be standard snap on breakers. Once the
>power has been inverted to AC, there is no
>reason to require anything other than standard code requirements.
>
>Drake Chamberlin
>Athens Electric LLC
>OH License 44810
>CO License 3773
>NABCEP Certified Solar PV
>740-448-7328
><http://athens-electric.com/>http://athens-electric.com/
>
>At 11:31 PM 10/10/2016, you wrote:
>
>My students we just today complaining about the
>access to wires on the panel mount breakers. The
>lug idea with separators might be a fix. It
>definitely needs to be done differently. In
>class We added another inverter to our package
>and trying to install another 175A breaker was a
>pain. We have a few other DC breakers in there
>already. The whole cabinet is basically inaccessible.
>
>Jesse Dahl
>
>NABCEP PV Installation Professional
>IBEW Local 292 - Electrician
>Electrical/Solar PV Instructor - HCC
>
>Sent from my iPhone
>
>On Oct 10, 2016, at 9:40 PM, Jerry Shafer
><<mailto:jerrysgarage01 at gmail.com>jerrysgarage01 at gmail.com > wrote:
>
>
>You might want to look at the square D QO
>breaker line some are dc rated and voltage rated and are panel mounted.
>Jerry
>
>On Oct 10, 2016 3:00 PM, "jay"
><<mailto:jay.peltz at gmail.com>jay.peltz at gmail.com> wrote:
>Iâ ll chime in here.<
>Yes the GSLC is a piece of junk.Â
>However it is UL listed for the job. And while
>you could put together something that would work
>with Airpax breakers together, but it wouldnât be UL.
>
>What I do is to swap out all the wires to Arctic
>ultra flex. This allows much better movement
>of the wires with significantly less stress on
>the terminals.  And if you want to not attach
>wires to the back of the breakers then you can
>and Iâve seen outback do it,it, install lay
>in lugs facing outwards so you can use a
>screwdriver or allen key on them. Allows for
>installation and removal of wire without removal
>of the breaker or the plate/breakers. With
>thimbles of course. And I canât find them but
>I know they make them, shielields that fit
>between each breaker so the lay in lugs are insulated.
>jay
>peltz power
>
>
>
>On Oct 10, 2016, at 4:40 PM, William Miller
><<mailto:william at millersolar.com>william at millersolar.com > wrote:
>Chris:
>Â
>Thank you for the reply. I think you
>misunderstand me. We always use the GSLC
>cabinets. I just donât like the design
>conceptept that clutters the cabinet with AC and
>DC breakers that are difficult to access and
>block other components. See photo below of a
>prewired GSLC Cabinet we were asked to work in. Not a good scenario.
>Â
>We have created an installation standard using
>the GSLC that minimizes the problems inherent
>with the design. We run all AC leads to
>adjacent load centers and we try to minimize the
>DC breakers in the cabinet. It is our goal to
>completely eliminate all breakers from the
>removable dead-front. I think it is pretty
>self-explanatory why one would not prefer to
>make connections in a hard to reach location.
>Â
>Our goal is to constantly improve our
>installation procedures to create better, safer
>and more efficient installations.Â
>Â
>Also, I donât need someone to instructuct me
>on how to make a âfinishedâ looking ing
>install. If you are familiar with my work you
>know it is as clean as it gets. Review my web
>site. Below is but one example of one of our installs.
>Â
>And lastly, âsuck it upâ is nos not a very
>complimentary phrase. Please, letâs ks keep it professional.
>Â
>Sincerely,
>Â
>William Miller
>Â
><image007.jpg>
>Figure 1 Factory wired GSLC
>Â
><image008.jpg>
>Figure 2 Miller Solar installed GSLC..
>Â
><image009.jpg>
>Lic 773985
><http://www.millersolar.com/>millersolar.com
><tel:805-438-5600>805-438-5600
>Â
>From: RE-wrenches [
>mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Chris Mason
>Sent: Monday, October 10, 2016 3:40 PM
>To: RE-wrenches
><<mailto:re-wrenches at lists.re-wrenches.org> re-wrenches at lists.re-wrenches.org>
>Subject: Re: [RE-wrenches] PV Recombiner
>Â
>The GSLC gives the system a nice finished
>appearance that the customer will understand.
>Suck it up and live with the imperfect world we function in.
>Â
>On Mon, Oct 10, 2016 at 5:55 PM, William Miller
><<mailto:william at millersolar.com>william at millersolar.com > wrote:
>
>Friends:
>Â
>I am looking for a PV recombiner. I need to
>accept the outputs from 3 remote PV Combiners,
>send those outputs through GFP circuit breakers,
>into charge controllers, back thorough breaker,
>into a bus bar, through a main breaker and onto a large battery bank.
>Â
>I am using 2 Outback Radian inverters, but I
>refuse to install DC breakers on their
>dead-front because wiring to studs facing away
>from the front is an inferior
>design. Furthermore, I see no need to run PV
>circuits through the GSLC cabinets.
>Â
>I looked at the Midnite MNDC15 but again, these
>use panel mounted breakers with studs on the back.
>Â
>Anyone know of a more thoughtfully designed PV recombiner?
>Â
>Thanks in advance,
>Â
>William Miller
>Â
>Â
><image003.jpg>
>Lic 773985
><http://www.millersolar.com/>millersolar.com
><tel:805-438-5600>805-438-5600
>Â
>
>_______________________________________________
>List sponsored by Redwood Alliance
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>Change listserver email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>Check out or update participant bios:
><http://www.members.re-wrenches.org/>www.members.re-wrenches.org
>
>Â
>Â
>--
>Chris Mason
>NABCEP Certified Solar PV Installer
>Solar Design Engineer
>Generac Generators Industrial technician
>Â
><http://www.cometenergysystems.com/>www.cometsolar.com
><tel:264.235.5670>264.235.5670
><tel:869.662.5670>869.662.5670
>Skype: netconcepts
>_______________________________________________
>List sponsored by Redwood Alliance
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>Change listserver email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>Check out or update participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>Â
>_______________________________________________
>List sponsored by Redwood Alliance
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>Change listserver email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>Check out or update participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>
>List-Archive:
><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>
>List-Archive:
><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
><http://www.members.re-wrenches.org/>www.members.re-wrenches.org
>
>Â
>
><https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
>Avast logo
>
>
>This email has been checked for viruses by Avast antivirus software.
><https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>www.avast.com
>
>Â
>Content-Type: image/jpeg; name="image003.jpg"
>Content-Disposition: inline; filename="image003.jpg"
>Content-ID: <image003.jpg at 01D2247C.ED0247E0>
>X-Attachment-Id: 53cec85809fc3170_0.1
>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20161012/d89dcb0f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 20f86209.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20161012/d89dcb0f/attachment.jpg>
More information about the RE-Wrenches
mailing list