Jerry,
I don't think that QOs or QOUs would work. I believe that all are rated=20
only to 50V DC, unless that longtime dual rating has recently changed.=20
As the Radian is only available in 48V, any DC conductors would exceed=20
this.
Allan

*Allan Sindelar*
allan at sindelarsolar.com <mailto:allan at sindelarsolar.com>
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*

**

On 10/10/2016 8:40 PM, Jerry Shafer wrote:
>
> You might want to look at the square D QO breaker line some are dc=20
> rated and voltage rated and are panel mounted.
> Jerry
>
>
> On Oct 10, 2016 3:00 PM, "jay" <jay.peltz at gmail.com=20
> <mailto:jay.peltz at gmail.com>> wrote:
>
>     I=E2=80=9Dll chime in here.
>
>     Yes the GSLC is a piece of junk.
>     However it is UL listed for the job. And while you could put
>     together something that would work with Airpax breakers together,
>     but it wouldn=E2=80=99t be UL.
>
>     What I do is to swap out all the wires to Arctic ultra flex.  This
>     allows much better movement of the wires with significantly less
>     stress on the terminals. And if you want to not attach wires to
>     the back of the breakers then you can and I=E2=80=99ve seen outback d=
o it,
>     install lay in lugs facing outwards so you can use a screwdriver
>     or allen key on them.  Allows for installation and removal of wire
>     without removal of the breaker or the plate/breakers.  With
>     thimbles of course. And I can=E2=80=99t find them but I know they make
>     them, shields that fit between each breaker so the lay in lugs are
>     insulated.
>
>     jay
>     peltz power
>
>
>>     On Oct 10, 2016, at 4:40 PM, William Miller
>>     <william at millersolar.com <mailto:william at millersolar.com>> wrote:
>>
>>     Chris:
>>
>>     Thank you for the reply.  I think you misunderstand me.  We
>>     always use the GSLC cabinets.  I just don=E2=80=99t like the design
>>     concept that clutters the cabinet with AC and DC breakers that
>>     are difficult to access and block other components.  See photo
>>     below of a prewired GSLC Cabinet we were asked to work in.  Not a
>>     good scenario.
>>
>>     We have created an installation standard using the GSLC that
>>     minimizes the problems inherent with the design.  We run all AC
>>     leads to adjacent load centers and we try to minimize the DC
>>     breakers in the cabinet.  It is our goal to completely eliminate
>>     all breakers from the removable dead-front.  I think it is pretty
>>     self-explanatory why one would not prefer to make connections in
>>     a hard to reach location.
>>
>>     Our goal is to constantly improve our installation procedures to
>>     create better, safer and more efficient installations.
>>
>>     Also, I don=E2=80=99t need someone to instruct me on how to make a
>>     =E2=80=9Cfinished=E2=80=9D looking install. If you are familiar with=
 my work you
>>     know it is as clean as it gets.  Review my web site. Below is but
>>     one example of one of our installs.
>>
>>     And lastly, =E2=80=9Csuck it up=E2=80=9D is not a very complimentary=
 phrase.=20
>>     Please, let=E2=80=99s keep it professional.
>>
>>     Sincerely,
>>
>>     William Miller
>>
>>     <image007.jpg>
>>
>>     Figure 1 Factory wired GSLC
>>
>>     <image008.jpg>
>>
>>     Figure 2 Miller Solar installed GSLC..
>>
>>     <image009.jpg>
>>     Lic 773985
>>     millersolar.com <http://www.millersolar.com/>
>>     805-438-5600 <tel:805-438-5600>
>>
>>     *From:*RE-wrenches
>>     [mailto:re-wrenches-bounces at lists.re-wrenches.org
>>     <mailto:re-wrenches-bounces at lists.re-wrenches.org>]*On Behalf
>>     Of*Chris Mason
>>     *Sent:*Monday, October 10, 2016 3:40 PM
>>     *To:*RE-wrenches <re-wrenches at lists.re-wrenches.org
>>     <mailto:re-wrenches at lists.re-wrenches.org>>
>>     *Subject:*Re: [RE-wrenches] PV Recombiner
>>
>>     The GSLC gives the system a nice finished appearance that the
>>     customer will understand. Suck it up and live with the imperfect
>>     world we function in.
>>
>>     On Mon, Oct 10, 2016 at 5:55 PM, William Miller
>>     <william at millersolar.com <mailto:william at millersolar.com>> wrote:
>>>     Friends:
>>>
>>>     I am looking for a PV recombiner.  I need to accept the outputs
>>>     from 3 remote PV Combiners, send those outputs through GFP
>>>     circuit breakers, into charge controllers, back thorough
>>>     breaker, into a bus bar, through a main breaker and onto a large
>>>     battery bank.
>>>
>>>     I am using 2 Outback Radian inverters, but I refuse to install
>>>     DC breakers on their dead-front because wiring to studs facing
>>>     away from the front is an inferior design.  Furthermore, I see
>>>     no need to run PV circuits through the GSLC cabinets.
>>>
>>>     I looked at the Midnite MNDC15 but again, these use panel
>>>     mounted breakers with studs on the back.
>>>
>>>     Anyone know of a more thoughtfully designed PV recombiner?
>>>
>>>     Thanks in advance,
>>>
>>>     William Miller
>>>
>>>     <image003.jpg>
>>>     Lic 773985
>>>     millersolar.com <http://www.millersolar.com/>
>>>     805-438-5600 <tel:805-438-5600>
>>>
>>>
>>>     _______________________________________________
>>>     List sponsored by Redwood Alliance
>>>
>>>     List Address:RE-wrenches at lists.re-wrenches.org
>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>     Change listserver email address & settings:
>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>     <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.o=
rg>
>>>
>>>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenc=
hes.org/maillist.html
>>>     <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/mail=
list.html>
>>>
>>>     List rules & etiquette:
>>>     www.re-wrenches.org/etiquette.htm
>>>     <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>     Check out or update participant bios:
>>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>
>>
>>
>>     --
>>     Chris Mason
>>     NABCEP Certified Solar PV Installer=E2=84=A2
>>     Solar Design Engineer
>>     Generac Generators Industrial technician
>>
>>     www.cometsolar.com <http://www.cometenergysystems.com/>
>>     264.235.5670 <tel:264.235.5670>
>>     869.662.5670 <tel:869.662.5670>
>>     Skype: netconcepts
>>     _______________________________________________
>>     List sponsored by Redwood Alliance
>>
>>     List Address: RE-wrenches at lists.re-wrenches.org
>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>>     Change listserver email address & settings:
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>     <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.or=
g>
>>
>>     List-Archive:
>>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/mailli=
st.html
>>     <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maill=
ist.html>
>>
>>     List rules & etiquette:
>>     www.re-wrenches.org/etiquette.htm
>>     <http://www.re-wrenches.org/etiquette.htm>
>>
>>     Check out or update participant bios:
>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>     <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillis=
t.html
>     <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/mailli=
st.html>
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.o=
rg/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.=
org/attachments/20161010/4d681d47/attachment.htm>


More information about the RE-Wrenches mailing list