[RE-wrenches] Fire fighters safety class

Dan Fink danbob88 at gmail.com
Wed Sep 21 11:55:34 EDT 2016


Hi charles, all.....yes, foam is both not opaque enough and slides off.
Blue tarps / thin tarps are not either....only thick or canvas works....and
what if the wind blows it off during the response?

I recommend the irec / iaff Web class highly, it uses all the new UL data
and  It covers nozzles patterns vs distance and voltage. Big takeaway on
that.....Ok to put water on pv from even 10 feet away, but do NOT direct
water at electrical enclosures, inverters etc

On Sep 21, 2016 6:39 AM, "Charles Picard" <cpicard at solarcity.com> wrote:

> Hi Dan,
>
>
>
> I’ll try to stop short of playing armchair firefighter here, and stick to
> what legitimate data is available. I follow most of the prominent
> Firefighter trade rags, and while there is some good technical content,
> there are also a fair amount of opinion pieces.
>
>
>
> The UL study linked earlier is typically the basis for any credible
> guidance on tactics or strategies, largely because there has been very
> little research done in the U.S.. In section 9 of that document you’ll find
> the analysis of the de-energizing experiments conducted.  These quotes
> stand out to me:
>
>
>
> 1.       “It was the consensus of those witnessing this experiment that
> this Class A foam was generally ineffective in blocking what little
> illumination the sun was providing that day.”
>
> 2.       “The application of ordinary Class A foam with a compressed air
> foam system did not prove to be effective or reliable in blocking sun to an
> array of PV modules.” (Note:  VT is likely to have much steeper roofs than
> used in these tests.)
>
> 3.       “…firefighting foam should not be relied upon to block light.” –
> Section 14
>
>
>
> You bring up a great point about the rank-and-file firefighter needing
> something quick and effective. Foam may be quick, but we would never say
> with confidence it is safe and effective. (How does an “average Fire
> Fighter” confirm that hypothetical 20Vdc?) I’d also ask that we start first
> by examining the need…Why would the firefighters need to de-energize the
> array during active fireground operations? Are those scenarios both
> plausible and likely?
>
>
>
> As a practical matter, de-energizing the array itself is going to be most
> important post-incident. This is admittedly a gap in coverage in this
> country. “Board-up”, or salvage companies may not be trained to make these
> systems 100% safe, so each Fire Department is left to seek out a local PV
> professional to offer guidance.
>
>
>
> Another document that may serve as a blueprint for developing standard
> procedures is here: http://www.nfpa.org/news-and-
> research/fire-statistics-and-reports/research-reports/for-
> emergency-responders/fireground-operations/fire-
> fighter-safety-and-response-for-solar-power-systems
>
> The bibliography is quite extensive.
>
>
>
> Happy Reading!
>
>
>
>
>
> *Charles Picard*
> Sr. Compliance Engineer | SolarCity <http://www.solarcity.com>
> -----------------------------------------------------------------------
> t:    518.380.6628
> m:  508.965.0144
>
> RI A-004714 REPC-119, CA CSLB 888104, MA HIC 168572/EL-1136MR. Click here
> <http://www.solarcity.com/company/contractor-licenses> to view our
> complete list of license numbers by state.
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160921/0cd662fc/attachment.htm>


More information about the RE-Wrenches mailing list