[RE-wrenches] Odd monitor readout Trace 4024

Brian Teitelbaum bteitelbaum at aeesolar.com
Thu Sep 15 20:05:14 EDT 2016


HA!



Looks like a scrambled brain. I can relate



As Allan said, shut off the main DC breaker (should be a 250A) and wait for
a minute of two to turn it back on. That may or may not work, but if it
does you will have to reset any custom programming, such as the battery
charging setpoints. Those inverters did not have non-volatile memory.



Oh, and be aware that many of these systems had the charge controller
output connected on the inverter side of the big breaker, so when you shut
off the breaker it would disconnect the battery, but not the charge
controllers, from the inverter. If that is the setup, but sure to switch
off the charge controllers also



Brian

AEE Solar



*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *RM You
*Sent:* Thursday, September 15, 2016 4:11 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Odd monitor readout Trace 4024



Has anyone seen this kind of readout on a Trace 4024 inverter. Unit is
functioning but access to the menu is unavailable and I’m wondering if it’s
a monitor failure or something else. I did a factory reset but got the same
thing.





Ron Young
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160915/5e267408/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 108278 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160915/5e267408/attachment.jpg>