[RE-wrenches] Splices in service panel

Mark Westbrock westbrock at positiveenergysolar.com
Fri Sep 9 08:49:23 EDT 2016


Hi Mac,

Our strictest local inspector allows us to do just what you are describing,
per NEC 312.8.  For the label described in 312.8(3), we make a custom label
that reads:

"Warning: This panel contains feed-through conductors.  OCPD for these
feed-through conductors are located ..." and then indicate physical
location of new subpanel (e.g. directly below this panel, etc.).

I hope that helps.

Cheers,

Mark
----
Mark Westbrock|  VP, Branch Manager |  Employee Owner
NABCEP™ Certified PV Installation Professional
NABCEP™ Certified
Technical Sales Professional
NM EE98J Licensed Electrician
510 S. Main St., Las Cruces, NM 88001
cell  575.640.2432 |  office  575.524.2030
mw at PositiveEnergySolar.com  <Your.Email at PositiveEnergySolar.com>
www.PositiveEnergySolar.com <http://www.positiveenergysolar.com/>



>> On Thu, Sep 8, 2016 at 8:00 PM, Mac Lewis <maclewis1 at gmail.com> wrote:
>>
>>> Hello wrenches,
>>>
>>> We run into many scenarios where we are locating a critical load panel
>>> adjacent to an existing service to make it easy to move the loads.  I've
>>> always taken it for granted (as have the electricians that we use) that we
>>> can't do a splice in the main panel and extend the load wiring to the
>>> critical load panel.  Is there code violation for doing a splice in the
>>> main panel and extending the leads to the critical panel?  You would be
>>> treating the service panel as a pass-trough/splice box for those critical
>>> loads.
>>>
>>> It makes me wonder because of all of the prewired transfer switch
>>> packages with wire whips already attached that seem to be designed to do
>>> just that.
>>>
>>> Code references would be appreciated.
>>>
>>> Thanks
>>>
>>> --
>>>
>>>
>>>
>>> Mac Lewis
>>>
>>> *"Yo solo sé que no sé nada." -Sócrates*
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: http://www.mail-archive.com/re
>>> -wrenches at lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>>
>>
>> --
>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160909/f429ffe4/attachment.htm>


More information about the RE-Wrenches mailing list