[RE-wrenches] Splices in service panel

Ray Walters ray at solarray.com
Thu Sep 8 20:13:04 EDT 2016


Hi Mac;

I'm not sure I understand how you would extend the wires without 
splicing. BTW you only need to extend the hots, not the neutrals or 
grounds.
*NEC 312.8* sets a cross sectional area limit of 75% for the splices and 
wires inside an OCPD Enclosure.
I just found these inline splices to use instead of the infamous wire 
nut: http://www.idealindustries.co.uk/product/12/557/67825/.html
These should make for a cleaner install, and take less precious space, 
but I haven't tried them yet.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 9/8/2016 6:00 PM, Mac Lewis wrote:
> Hello wrenches,
>
> We run into many scenarios where we are locating a critical load panel 
> adjacent to an existing service to make it easy to move the loads.  
> I've always taken it for granted (as have the electricians that we 
> use) that we can't do a splice in the main panel and extend the load 
> wiring to the critical load panel.  Is there code violation for doing 
> a splice in the main panel and extending the leads to the critical 
> panel?  You would be treating the service panel as a 
> pass-trough/splice box for those critical loads.
>
> It makes me wonder because of all of the prewired transfer switch 
> packages with wire whips already attached that seem to be designed to 
> do just that.
>
> Code references would be appreciated.
>
> Thanks
>
> -- 
>
>
>
> Mac Lewis
>
> *
>
> "Yo solo sé que no sé nada." -Sócrates
>
> *
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160908/8a7771bf/attachment.htm>


More information about the RE-Wrenches mailing list