Wrenches
Better pic
On Sep 5, 2016 4:52 PM, "Jerry Shafer" <jerrysgarage01 at gmail.com> wrote:
> To my fellow wrenches
> It comes up every so often and with DC, I will not use, approve or pass
> any wire nuts on any DC side. Some say its OK but the facts are they will
> fail, this connection was just six years and when l opened the junction box
> it was glowing and by the looks of it has for some time. There are 8
> strings 2 per string and thats a 12.5 % failure rate (the other one was
> completely distroyed) not to mention the fire hazard in a PVC junction box.
> Please pass this along and tell everyone to stop using these.
> Jerry
>