[RE-wrenches] SMA Tripower

Brian Mehalic brian at solarenergy.org
Thu Sep 1 00:24:09 EDT 2016


Hey Wrenches-
Just a heads up on the SMA Tripower - I like the inverter, but you gotta
read the install manual!

Spec sheet says 24 A continuous output current for the 20 kW Tripower.
Install manual (and tech support) says 24.1.  That  extra .1 A takes you
from a 30 A to a 35 A breaker.

Of course you should follow the install manual not the specs.  But what
about the label on the side of the inverter?  Well I've seen more than a
handful that are labeled with a flat-out 24 Aac output current.  What's an
installer or inspector to do besides hope mfg's can get their numbers in
order?

Upon closer examination, most of the STPs are 0.1 A higher than their spec
sheet per the install manual - it doesn't really make a difference on the
12 or 15 kW models - just the 20 where you have to go up 1 standard OCPD
size.  Pretty sure there's lots of 20 kW units out there backfeeding a 30 A
breaker.  Hmmmmm....

Brian Mehalic
NABCEP Certified Solar PV Installation Professionalâ„¢ R031508-59
520.204.6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160831/cfe82e39/attachment.htm>