[RE-wrenches] Made three shut down

Lones Tuss ltuss at outbackpower.com
Mon Aug 29 14:48:35 EDT 2016


Hi Dana
If you are in a lightning prone area surge protection is a must.
OutBack has a surge protection device that mounts directly on the inverter (see the link below).
http://www.outbackpower.com/downloads/documents/Hardware_Accessories/flexware_surge_protector/fw_sp_specsheet_english.pdf
Midnite makes surge protection devices can that be added through-out the system.
The Mate3 will not be negatively affected by surge protection.
Lightning protection is a controversial subject and is certain to invoke strong opinions.
Lightning protection strategically placed throughout an electrical system can only help.
Unfortunately I don’t think anyone is willing to offer a 100% guarantee of protection.




Lones Tuss
Applications Engineer
OutBack Power Technologies
17825 59th Ave NE, Suite B, Arlington, WA 98223
360.618.4383 Office | 425.213.8794 Cell
www.outbackpower.com<http://www.outbackpower.com/>

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dana Solar work
Sent: Saturday, August 27, 2016 3:04 PM
To: RE-wrenches
Subject: [RE-wrenches] Made three shut down

I have a client who's Mate three basically seized up, Lost its programming and I did a manual reprogram which it then proceeded to lose that also. I called Outback tech they suggested I reset to factory default and then reprogram which due to the fact I had to leave Colorado for 48 hours I can't do it now the system is complete shut down.
The tech at Outback said that lightning strikes nearby could exhibit an EMP effect on the mate or even static that would cause this to happen.
Is anyone aware of any filtration/ surge protection device that might work without interfering with the maid threes function and accommodate an ethernet cable?
Phil Underkuffler at outback if you want to chime in on this I'd appreciate it and since it is lightning season in Colorado I'm sure other people may appreciate it too
From the road in Idaho thanks

Dana Orzel 2087217003
Great Solarworks Inc - NABCEP#051112-136
E-dana at solarwork.com<mailto:E-dana at solarwork.com> c-2087217003
"Responsible Technology for Responsible People since 1988"
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160829/4c0cd0c6/attachment.htm>


More information about the RE-Wrenches mailing list