[RE-wrenches] Low array voltage stumper on legacy system
Allan Sindelar
allan at sindelarsolar.com
Fri Aug 26 02:12:08 EDT 2016
Steve,
Yes, in the same sequence: 75.5V, 73.8V, 73.9V, 74.0V. All just about
what I'd expect.
Brian,
I have seen that with KC120s over the years - good Voc and Isc but no
MPP. That's a known failure that Kyocera (to their credit) continues to
warrant 15 years out. But I haven't seen it with the many 75W BPs we
installed in that same time period. So it's possible, but unlikely,
especially with all four strings behaving in a similar manner.
Thank you. I'm off on field work now, will respond to any more replies
tomorrow.
Allan
On 8/25/2016 8:24 AM, Steve Bell wrote:
> Hello Allan,
>
> Did you check the Voc of each string? Is it possible that there could
> one or more shorted bypass diodes in the modules?
>
> Just a thought.
>
> Steve Bell
> Morningstar tech support
>
> On Thu, Aug 25, 2016 at 8:04 AM, Allan Sindelar
> <allan at sindelarsolar.com <mailto:allan at sindelarsolar.com>> wrote:
>
> Wrenches,
> Here's one I haven't seen before. 1997 grid-tie battery backup
> system that was one of my first, although actual installation was
> by another before I was licensed. 16 BP 275, 36-cell 12V modules,
> the standard of that time. Early Outback MX60 replaced C40 around
> 2005; array rewired to four 48V strings of four modules at that
> time, serving a 24V battery bank. Tested with an end-of-life
> 9-year-old AGM battery bank in the system, but in Sell mode with a
> 26.4V Sell voltage setpoint.
>
> At 11 am, 68ºF, 900W/m^2 on the Daystar, with the array under
> charge, I measured 3.5A, 3.4A, 2.4A, and 3.6A. Short-circuiting
> each string, I measured 4.0A, 3.7A, 3.8A, and 3.7A. Original
> rating was 4.45A, so except for the third string, current is what
> I'd reasonably expect from 20-year-old module degradation.
> However, watching the periodic MPPT sweep from the MX60 at the
> array, the maximum power point voltage for the entire 48V array
> settled at 14.6A at 37.2V, or about 540 watts from a 1,200W
> (originally rated) array.
>
> I have commonly seen the current reduce substantially with
> age-related degradation, while the MPP voltage remains fairly
> close to original. I have never seen the voltage drop this far -
> an average of 9.3V MPP per each 12V module. All of the cells are
> seriously browned. I have other systems out there with the same
> modules of similar age that don't exhibit this weird behavior. Can
> anyone help me understand why the MPP voltage would drop so far
> below what is typical?
>
> There is a slight possibility of corroded buried input conductors,
> because of a serious but corrected issue of galvanic corrosion
> from a ground fault (a Romex connector pinching a conductor and
> allowing seepage to ground). This was corrected years ago, but the
> input conductors were direct burial for ~100' and there was never
> a bonding conductor between the array and the house, so there is a
> potential for corrosion damage. However, the voltage measured at
> both ends while charging was identical, so I think that would
> indicate that high conductor resistance isn't the issue.
>
> As usual, thank you for the collective and individual wisdom
> shared here.
> Allan
> --
>
> *Allan Sindelar*
> allan at sindelarsolar.com <mailto:allan at sindelarsolar.com>
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> *505 780-2738 <tel:505%20780-2738> cell*
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160826/6aa61666/attachment.htm>
More information about the RE-Wrenches